design central heating circuit for rayburn 355s

Joined
22 Oct 2013
Messages
2
Reaction score
0
Country
United Kingdom
Just swapped old non pumped rayburn royal that managed to heat DHW and 2 small rads as heat sinks.
Now have much beefier 355 model so trying to design a system that will work with minimal interference to existing (upstairs) gravity fed tank and rads. Consulted all the usual channels
My question is that I want to put a rad (last in line) in my office which is below level of rayburn. Where does the pump need to go and will it work?
I'd like to get it right first time, hence the question. I could have the rad mounted half way up the wall to keep same level but it would look silly and loose shelf space...
 
Sponsored Links
A radiator below the boiler level is no problem. Your pump is not a pump, but a circulator, and as such, as long as you have no airlocks, it will circulate through the whole circuit.
Best place for the pump is after the cold feed, but with just a gravity circuit, your pipework may need some adapting to resemble a good punped circuit. Have a look at some of the design examples you have loked at and see how yours compares
 
Thats a great help, thanks.
I'd previously had a radiator in the cellar which never worked properly and I assumed its location was part of the problem.
I am a bit fixated with pump on the return just before the injector tee, couple of feet from the boiler, as that's where most of diagrams show it. With it being solid fuel I have to keep the gravity side and reluctant to interfere as it worked so well, after several attempts ;)
 