No, it will not wear out any faster without electrons travelling thru it. By the way, what was the size (in Amps) of the breaker?
The reason I am asking is because, providing it is (therefore was) adequate for the existing cable run it should be OK for 1 twin socket under all conditions but if latter additions are added then if it becomes a radial or a ring there are some considerations (32A if a bog standard ring and 20A if a bog standard radial of 2.5 T & E each but 4.0 T & E as a radial would still allow you 32A anyway providing that cable lengths are not excessive) if it`s a 40A or 45A say on the existing set up and the existing cable was fit for it then one only twin socket should be fine anyway