Hi,
I've applied for G99 for 16kW solar PV and battery storage all behind a G100(2) export limitation device set to 0kW (zero export). Single phase 100a supply.
DNO has come back asking for a large payment (multiple thousands) for network and supply upgrades as they say this amount of generation will lead to unacceptable voltage rise (over 12%) in MY property due to the length and age of my supply cable. (1940 house in a residential part of a city - not remote or rural).
I don't understand. I thought significant voltage rise would only occur when exporting (due to the need to be 'higher' than the grid and overcome resistance of the supply cable). If 0kW G100 export limit surely there should be no generation limit?
Is DNO trying to pull a fast one?
Cheers for any comments.
Joe
I've applied for G99 for 16kW solar PV and battery storage all behind a G100(2) export limitation device set to 0kW (zero export). Single phase 100a supply.
DNO has come back asking for a large payment (multiple thousands) for network and supply upgrades as they say this amount of generation will lead to unacceptable voltage rise (over 12%) in MY property due to the length and age of my supply cable. (1940 house in a residential part of a city - not remote or rural).