Social services have kindly paid for the intercom at my mothers door to be mains powered instead of battery.
The contractor arrived and fitted a 12vac transformer to replace the original 12vac transformer in spite of me telling them many times it needed 12vdc.
They then returned to swap to DC but could not source a 12vdc wall mounted transformer so fitted a 13A socket and a plug in inverter to replace it.
Today I decided to test the socket. ELI at 0.23 ohms so earth is connected but testing the RCD at 30ma and 1/2, full and 5 times both positive and negative all fail to trip the RCD clearly taken from the non RCD side of the consumer unit.
There is no label to say for door intercom only but to comply with regulations really that's all that would be required. Also no minor works or installation certificate issued.
Socket is under stairs and my mother in her wheel chair could never access it.
So in real terms no real danger just a little sloppy in the way they have done it. A simple label saying for door intercom only and a minor works certificate and it would comply.
So should I.
1) Do nothing.
2) Phone contractor.
3) Phone social services.
What does the team think?
The contractor arrived and fitted a 12vac transformer to replace the original 12vac transformer in spite of me telling them many times it needed 12vdc.
They then returned to swap to DC but could not source a 12vdc wall mounted transformer so fitted a 13A socket and a plug in inverter to replace it.
Today I decided to test the socket. ELI at 0.23 ohms so earth is connected but testing the RCD at 30ma and 1/2, full and 5 times both positive and negative all fail to trip the RCD clearly taken from the non RCD side of the consumer unit.
There is no label to say for door intercom only but to comply with regulations really that's all that would be required. Also no minor works or installation certificate issued.
Socket is under stairs and my mother in her wheel chair could never access it.
So in real terms no real danger just a little sloppy in the way they have done it. A simple label saying for door intercom only and a minor works certificate and it would comply.
So should I.
1) Do nothing.
2) Phone contractor.
3) Phone social services.
What does the team think?