Do I need a second pump

Joined
14 Oct 2004
Messages
23
Reaction score
0
Country
United Kingdom
I Have a Glow worm 30CXI combi boiler fitted in my loft space. All the radiators heat up ok apart from the last 2 on the run and they very bottom of the house one in the cellar and one on ground floor. I can get them to heat up ok if I turn 2 other rads off on the ground floor, I have balanced the rads as well.

Do I need another pump fitted on the ground floor due to the fact the boiler is fitted in the loft and the drop is to far to circulate the water?

If so can you recommend the best pump and location.

Many thanks
 
Sponsored Links
Could you expand on your answer please, what can I do then?
 
Keep balancing. Small rads near the boiler will only need to be open a fraction of a turn.
If the pipes are undersized it may not manage, in which case talk to GW.
 