Double Socket Addition in Attic

Hi, if the socket has it's own MCB rated at 16a or 20a you can add your socket as you intend to do using 2.5mm.

Kind regards,

DS

To spite all discussion :LOL::LOL:

In this case less is more, the poor OP why can't you just answer the F….. question !

DS
 
Sponsored Links
If the MCB is a B16, and if the cable is 2.5mm² (or, in fact, probably even if it were 1.5mm²), then (despite all the discussion that there's been) there are absolutely no problems with what you plan to do.

Kind Regards, John

Thanks man

Very interesting stuff once you get started all this !!!
 