Double socket earth connection

I was once doing some decorating in my own house, where the wiring is pretty good, and changing singles for doubles. I had turned off the socket circuit for that floor, and tested a couple of sockets for dead.

While I was doing another, one of the wires came loose and I heard a faint tick.

That particular socket was on the circuit for another floor, God knows why.

The tick was the RCD tripping. Without a pigtail, it might not have done.

I am a bit less careless now in testing for dead.
 
I suppose it's true that in normal use a live wire does not contact a screw or backbox

Often.
 
For full disclosure, that was the 1995 version. That wording may have changed since then.
 
That wording may have changed since then.
Identical in the 2018 revision.

Most standards rarely change, and even when they do, the changes are either additions, or irrelevant modifications created for the sole purpose of being able to sell a new version.
 
Identical in the 2018 revision.
Thanks.

Also I have: "Between BS 1363-2:1995 and BS 1363-2:2023, the core technical requirements for earthing the fixing screws from the connected CPC (circuit protective conductor) terminal have not changed in substance, though the section was renumbered from Clause 10 to Clause 11 (Provisions for earthing)."

I believe that the US has a law stating that any standard quoted in government legislation must be available free of charge. One of the few things they got right, then.
 
I believe that the US has a law stating that any standard quoted in government legislation must be available free of charge. One of the few things they got right, then.
Same in the sailing or flying world, all the chart data is FOC in the USA unlike UK/ROW.

 
believe that the US has a law stating that any standard quoted in government legislation must be available free of charge. One of the few things they got right, then.
A search suggests that regulations only need to be "reasonably available" to interested parties—which courts have ruled does not automatically mean free.
 
A search suggests...
I suppose I am influenced by searching for some paid for spec and finding it republished for free on a us government site. To me it seems insane to require someone to comply with a law that they have to spend hundreds of pounds to understand. But maybe you don't agree.
 
10.2 All accessible metal parts of socket-outlets shall be in effective electrical contact with the earthing
socket contact, except that metal parts on, or screws in or through, non-conducting material, and separated
by such material from current-carrying parts in such a way that in normal use they cannot become live,
need not be in effective electrical contact with the earthing socket contact.

I suppose it's true that in normal use a live wire does not contact a screw or backbox

That doesn’t matter. The fixing screws are not “separated by [non-conducting] material from current-carrying parts” but only by an air gap. Therefore they do not fulfil the “except” clause, and must be earthed.

An example of something that would fulfil that clause would be a screw in a blind hole in the front face of the plastic.
 
it seems insane to require someone to comply with a law that they have to spend hundreds of pounds to understand.

You may find some of these documents in your local library, free of charge.

Fundamentally, standardisation documentation has not caught up with the internet age. See also academic journal publishing.
 
I believe that the US has a law stating that any standard quoted in government legislation must be available free of charge. One of the few things they got right, then.

The NEC is accessible FOC: https://blog.heatspring.com/the-2026-national-electrical-code-is-now-available-online-for-free/

They say "It’s important to note that this is read-only access – you can’t download or print the full code,". I suspect they probably mean you may not download or print... :sneaky:
 
That doesn’t matter. The fixing screws are not “separated by [non-conducting] material from current-carrying parts” but only by an air gap. Therefore they do not fulfil the “except” clause, and must be earthed.

Are fixing screws part of the socket?
 