Double socket off a 13a fused switch?
20 Mar 2009
Sheffield
While fitting our new kitchen i replaced a single unswitched socket for a double unswitched socket so that i could run a tumble dryer and washing machine from the same 13a fused spur. That fuse in the spur has just gone. I've replaced the fuse and its working again but is a dryer and washing machine likely to be too much for the spur/fuse?
It’s too much for 13A when on together
It’s also not sensible for them two items in the same double.
Some replanning required.
Why is the socket on a fused spur? There may be a good reasons such as a spur on a spur, but often for some reason people use a fused spur for a washing machine socket when a double pole switch is all that is needed.
I agree that a FCU is not required if it is feeding a socket for an appliance. But I always do(and I think it tends to be done this way by most) as I have too much experience of exactly the scenario outlined in the OP.
I found one situation where a single socket had been changed to a double and had 2 (unfused) adapters with 4 appliances plugged in.
But that could be done with any socket on the ring, and create problems.
There's no guarantee that the cables supplying any socket on a ring have as high a current-carrying capacity as a single 2.5mm² spur cable if the installation methods are different.
I thought all the derating factors had been taken into account, is this not so?
But at least it will have 2 cables feeding it. And this is exactly why I believe spurs should be:
A) not allowed, or
B) fused down, or
C) use a bigger cable.
Not sure what you mean.
Which may (allowably) have a CCC of only 20A, whereas a 2.5mm² spur cable from the same circuit might be 27A.
A) not allowed, or
B) fused down, or
Would you do that via a special removal of compliance with the general regulations on fault and overload protection, or would you change those fundamental principles?
I have gone through life under the impression that the ring final is a predetermined installation method which has all the circuit design principles taken into account including but not limited to derating factors.
It's perfectly feasible that a full load of 32A may be applied at any point of a ring, by that I mean there may be several sockets in close proximity with heavy loads, such as the kitchen. Are you saying this may be outside of the design parameters and therefore unsafe?
I would do this by applying circuit design principles, I would not consider a 2.5mm² radial on a 32A OCD to be a sensible design even if it only had a single 13A fuse on the end of it, however the blasé addition of such to a ring is considered to be conformist and safe. Indeed I have several incidents of such in my home, as it happens far fever than when I purchased but that's a different story.
Before anyone starts describing downstream fusing, I am very familiar with the principle within my control panel experience.
Do away with rings, then you can call the spurs something else - namely branches.
I do have some sympathy with the dislike of rings, however I personally have not encountered any significant problem in the 50 years I've had involvement with them. As such I have no real axe to grind for removal. As it happens I have recently changed 4x16A radials to 2x32A rings to upgrade stage lighting in a village hall.
To put this into context, I find that many new builds have a 12way grid plate with 6 switch & 6 fuse modules as the significant, if not total, load on a ring final.
That potential problem surely goes away if one installs a single socket for the appliance - in which case an FCU supplying it is certainly not needed, given the fuse in the {one and only} plug.
Kind Regards, John