It doesn't matter which room they're in, but that many sockets shouldn't be on a spur unless it is fused, when you can have as many as you like but you can't draw more than 13A total.
<various things>
Don't start superfluous posts until the OP's query has been satisfied.
Chill ….we all have at least one……… DSWhat else is revoking what I had previously said?
I'M SORRY I MENTIONED EXTENSION LEAD. I THOUGHT IT WAS FOR TELLIES ETC. - NOT WASHING MACHINES ETC.
You really want to watch more fighting?OK. Now... Shake hands and come out fighting.
You do them more than 70mm apart? Seems a bit far.I use a single gang box as a spacer when marking out.
A practical point is that if the socket boxes are so close together then the cable between them might just be in singles / t&E cores when it should be sheathed.
Or it's on a radial. Everyone has assumed (probably correctly) that it's an RFC on a 32A MCB (or 30A fuse) and wired in 2.5mm² T&E.It doesn't matter which room they're in, but that many sockets shouldn't be on a spur unless it is fused ...