Like to ask you lads a question re: a change of connected equipment.
Originally the CCU had a Hob and an Oven connected to it. The hob is going to be replaced with a gas unit but still needs a supply for the igniter.
Would I be correct in thinking that the flex to the hob will have to be connected via a FCU with a fuse in it to suit the flex size, or would it be OK to just terminate it directly into the 2nd cct on the CCU if I replace the flex with 2.5mm² or 4mm² cable ( if it'll fit of course ?
The existing Main Cable Feed is 6mm² through an above-worktop DP Cooker Switch via a 32A RCBO in the CU.
There is a socket on the Cooker Switch if that makes any difference.
Lastly, would any of this work be notifiable as I'm not really adding any new circuits ?