    in regards to the 2391 practical.....

    1, for the external earth fault loop impedance, do you disconnect the earth coming into the 3 phase db from the main earth terminal? have heard conflicting methods of this, some saying yes because of the pp's and some saying no because its a test board????

    2, similarilly, when doing the ze at the single phase cu do i disconnect the earth from the earth terminal in the single phase cu or leave it in??
     
  2. Sponsored Links
  3. Lectrician

    Lectrician

    Joined:
    18 Jul 2004
    Messages:
    8,515
    Thanks Received:
    406
    Location:
    Devon
    Country:
    United Kingdom
    If the single phase CU is a submain (don't recall one of my AM2?) - the you do a Zs (called a Zdb).


    For the main TP board, you should disconnect the earth from earth bar - I recall being able to do this by dropping a link on the bar. (as is required by bs7671 in fact).
     
  4. andy1984

    andy1984

    Joined:
    3 Aug 2006
    Messages:
    34
    Thanks Received:
    0
    Country:
    United Kingdom
    and can anyone confirm the proceedrure is

    measure L1-E,L2-E,L3-E and record the highest value as ze????

    and for fault current

    L1-E,L2-E,L3-E and then L1-N,L2,-N,L3-N . whichever reading out of the 6 gives the highest value is doubled and recorded. is this correct or have i missed something or got anything wrong???
     
  5. Spark123

    Spark123

    Joined:
    2 Jun 2005
    Messages:
    14,841
    Thanks Received:
    474
    Location:
    Cumbria
    Country:
    United Kingdom
    You've got it.
    Btw if your tester can do 400v tests you can use it L1-L2, L2-L3, L3-L1 as well. Don't need to double these.
     
  6. andy1984

    andy1984

    Joined:
    3 Aug 2006
    Messages:
    34
    Thanks Received:
    0
    Country:
    United Kingdom
    cheers spark. got a megger mft1502, believe it can do the 400v tests but ill check of course.

    does that mean i can not bother with any of the 6 tests and just do l1-l2,l1-l3,l2-l3 then because one of these will be the highest?
     
  7. Spark123

    Spark123

    Joined:
    2 Jun 2005
    Messages:
    14,841
    Thanks Received:
    474
    Location:
    Cumbria
    Country:
    United Kingdom
    I would say you still need to complete all the tests, the phase to phase are almost definately going to be higher than phase to neutral/earth unless there are a couple of reduced phase conductors upstream (unlikely I know).
     
  8. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
  9. Sponsored Links
Loading...

Share This Page