Electic shower power hunting

Joined
17 Jun 2011
Messages
1
Reaction score
0
Location
Wiltshire
Country
United Kingdom
I have just installed a new electric shower (9Kw) with a 40A mcb connected to a RCD and then to a 40A switch to control supply to shower via 6mm cable. When I turn on the shower the power hunts (on/off repeatedly), the mcb + rcd do not trip but the socket mcb does.

Help any ideas please.
 
Sponsored Links
I hope its 10mm² cable and not 6mm² :/

Depending on cable run, clipped, free, conduit, insulation etc.
 
Sponsored Links
Not even if flow valve is allowing some water through, then the overheat stat cuts out?
 