... one of the conditions for the omission of overload protection is that it is not where there is a fire risk (433.3).
You refer to 433.3 and it seems obvious that a kitchen should present a fire risk, so I have to agree with everything you say, as you have many times more understanding than me, so it got me reading the regs a bit more ...
I have also looked at Regulation 434, Protection against Fault Current - I have read 434.2 & 434.2.1 over and over.
434.2 says that where a cross-sectional area change takes place (causing a reduction in the CCC), a
device providing protecting against fault current shall be installed at the point where the reduction takes place.
434.2.1 says that 434.2 shall
not be applied to installations situated in locations presenting a fire risk ....
So if a kitchen is a fire risk, 434.2 should not be applied - and we know that many protective devices are located in kitchens where the csa is reduced (in fact we discussed installing a 13A FCU as an option).
434.2.1 says that a device for protection against fault current may be installed other than that specified in 434.2 provided that the point of reduction in cross-sectional area change and the protective device shall not exceed 3m.
Eureka - So the maufacturer is claiming that a kitchen does not represent a fire risk, this enables them to :
1. quote cable size appropriate to the power rating of the appliance with no regard for the breaker size.
2. tell you to use a cable of MAX 2m length obviating the need to put in
ANY protective device between the reduction in csa and the appliance, since you have up to 3m before you need to install a protective device.
3. quote a
minimum rating of 32A, because it is allowed to be higher (after all they are claiming overload isn't a consideration, it's only fault current that is a consideration).
I don't think any of their literature is wrong now - I think it's the stance they are taking regarding the appliance, and I presume after taking advice. I may not agree with it ...
PS - EFLI - Thanks for your patience, your thoughts on these obseravtions much appreciated.