i turned the main switch off and the Ampy Metering 5235A continued to flash 5 times a minute, my clamp on ammeter showing 0 amps
You mention that you have several CUs.
3, one at the meter, and two in the loft
It's great that you have a main switch that isolates the entire installation
Except that it obviously doesn't.
oh, it definitely does
I don't know where you are putting your clamp, it should be on the meter tails.
thats where its going
A true main switch should isolate the tails that come out of the meter before they go into any CU or Henley blocks. Does yours? You may have to pull off some of that boxing-in. It will be worth it.
Some Main Switches
View media item 820
View media item 819
the supply goes
cutout
¦
meter
¦
main consumer unit
¦ ¦
sub d/b1 sub db/2
the isolator is in the main consumer unit, this has two breakers in it supplying the two sub boards.