Electrics after a fire

What has @MickieMonday said that makes you believe that?

Domestic situation, VRI (cotton covered) = grip steel conduit, as in Eric's example photo -
.
1755270039815.png

What has the OP said, which might lead you to believe it might be the much more expensive installation of threaded conduit?
 
I had to google tncs. The explanation was a bit complex. All I really know is that there are only live and neutral behind the socket faceplates. They've never had a problem, so far.
could you send us some useful pictures?
Such as:
Inside several sockets switches etc
The fusebox showing the ends of the conduits and any earth wires or clamps please.
 
Wiring done by a moonlighting electrician from a nearby factory, possibly using materials he liberated from the stores?

I think most unlikely - when I've heard of TNC systems existing (and I've heard the same from two different 'grey beards' so I'm believing what I was being told*). The circuits were wired in single core MICC with the larger CSA of the sheath meaning the voltage drop on the PEN conductor was minimal. The instances were more commerial fit-out rather than industrial and it was done to save money (The idea of someone wiring something in MICC trying to save money sounds a bit silly in the modern world - but different times etc) I've heard of it being applied to both submains and also to final circuits as well. Even back then the engineer in charge had to get permission from the home office to install a PEN in a customers installation. The idea that someone would drag a drum off single core MICC off the site and start wiring mrs jones's sockets in it, with the increase in installation and termination time -No they'd just get someone to liberate a drum of twin & ecc from a more conventional job - they might actually make it to the pub on the saturday afternoon after finishing the private job.

More likely its just using the containment as earth, possibly with a fifty year DIY bodge to get past some some bad joints (possibly by someone who had heard about north amercian practices) , but no way was it intended that way

*It was never that widespread either, I'm yet to have have seen an example, despite having worked on plenty of installations wired in that sort of era, there is also the possibility that it was a localised practice or even in a number of jobs being done by the same contractor or being overseen by the same engineer.
 
I would say the question is more why was TN-C-S or the other name PME was ever allowed?
As I'm sure you actually know, "PME" is not "another name for TN-C-S", since they relate to totally different things. TN-C-S is only allowed if PME is present.
 
Surely not 'totally different'.
Why not? "TN-C-S" relates to how the DNO's earth is supplied to an installation - with a two-conductor feed and the earth derived from the neutral within the installation. "PME" means that the neutral of the DNO's final distribution circuit has at least one other connection to true earth in addition to the one at the transformer/substation. They are surely very different things, afren't they?
I am still puzzled by this. Could you explain please?
I'm also puzzled, because I thought I was just "stating facts" ...
Any supply could be configured within the installation as TN-C-S (i.e. the installation's 'earth' could be derived from the neutral within the installation {at the cutout}) - but that is surely only 'allowed' if the supply (distribution circuit) has been PMEd?
 
Why not? "TN-C-S" relates to how the DNO's earth is supplied to an installation - with a two-conductor feed and the earth derived from the neutral within the installation. "PME" means that the neutral of the DNO's final distribution circuit has at least one other connection to true earth in addition to the one at the transformer/substation. They are surely very different things, afren't they?

I'm also puzzled, because I thought I was just "stating facts" ...
Any supply could be configured within the installation as TN-C-S (i.e. the installation's 'earth' could be derived from the neutral within the installation {at the cutout}) - but that is surely only 'allowed' if the supply (distribution circuit) has been PMEd?
Again, there is also PNB. TN-C-S is not always PME.
 
There is also PNB (Protective Neutral Bonding).
There is, but I doubt that you'd ever see that in a domestic installation (and this is a DIY forum).

There isn't really any appreciable difference between 'PME' and 'PNB'. With PME, there is at least one further connection (in addition to the one at the transformer) between supply neutral and earth in the course of the DNO's distribution cable. With PNB, there is again (just) one additional connection between neutral and true earth, but that is "at" the installation.

Hence, if there was just one additional neutral-earth connection, it would be called PNB if that connection was located 'within' the installation, but PME if it were a few centimetres before it connected to the installation - i.e. essentially 'no difference'.
 
Again, there is also PNB. TN-C-S is not always PME.
There is, but I what I was writing (and have just posted) whilst you were writing that.

"PNB" is really just a subset of "PNB" (both requiring at least one 'additional N-E connection - the only difference {in the case of a single additional connection} being its location) - so one can really take "PME" to include PNB.
 
Why not? "TN-C-S" relates to how the DNO's earth is supplied to an installation - with a two-conductor feed and the earth derived from the neutral within the installation. .
As you say the earth is supplied to the installation [by the neutral]. I am not sure that is classed as within the installation.
Connecting exposed and extraneous-conductive-parts to the neutral within the installation is prohibited.

"PME" means that the neutral of the DNO's final distribution circuit has at least one other connection to true earth in addition to the one at the transformer/substation. They are surely very different things, aren't they?
So - PME is TN-C-S plus [at least] one other earth connection.
I wouldn't class that as totally different, would you?
In fact, within the installation it is exactly the same.

I'm also puzzled, because I thought I was just "stating facts" ...
Presumably not.

Any supply could be configured within the installation as TN-C-S (i.e. the installation's 'earth' could be derived from the neutral within the installation {at the cutout})
By the DNO - but I dispute that as being within - which is prohibited.

- but that is surely only 'allowed' if the supply (distribution circuit) has been PMEd?
I don't think so. If it hasn't been PMEd then it is TN-C-S.
 
As you say the earth is supplied to the installation [by the neutral]. I am not sure that is classed as within the installation.
You appear to be quibbling, I would say somewhat 'pedantically' about the terminology, and I'm not sure why.
Connecting exposed and extraneous-conductive-parts to the neutral within the installation is prohibited.
Well, in electrical terms that's obviously what one does - and in the cases of the bonding of extraneous-c-ps it's essentially literally what one does.
What is 'prohibited' (within a domestic installation) is connecting an exposed-c-p to a conductor which is a single 'combined N & E').
So - PME is TN-C-S plus [at least] one other earth connection.
Not really. PME is PME and is a feature of the distribution network, whereas TN-C-S relates to how the installation derives its 'earth'.
The supply to my house has been PMEd but I am certainly not using the supply as TN-C-S (and, at least theoretically, could not do so unless they provided the connection to their incoming neutral).
I wouldn't class that as totally different, would you?
Yes, I would.
By the DNO - but I dispute that as being within - which is prohibited.
As above, the only thing which is 'prohibited' is having conductors within an installation which are a 'combined N & E'. I think that makes sense, since it would mean that, even under non-fault conditions, exposed-c-ps in the installation would not all be at exactly the same potential.
I don't think so. If it hasn't been PMEd then it is TN-C-S.
I don't really understand what you are saying. If the supply hasn't been PMEd, then it is not 'allowed' to be used as TN-C-S
 