Why wouldn't you? As an EFLI tester draws around 25A it may operate a B6 mcb, Zs = Ze + (R1+R2) can also be used.
There is a requirement to IR test all circuits before energizing, wether you disconnect the smokes or join p&n together and test to earth is up to you. Have you got a copy of GN3?
They are just the same as any other circuit, you need to prove it will disconnect. I wouldn't touch the interconnection wire with any instrument with smokes connected though.
Measure Ze using ELFI tester!! Add this to your R1+R2 reading from the smoke circuit.
Ze for TN-S is max 0.8ohms. You need to verify this to confirm the earth has been connected.