Why the post about the steps, if you knew that no judgement is needed to determine that teetering on them is automatically illegal?
Aren't you a bit late for that?Before this thread decends into pointless gibberish:-
As a piece of generic advice that's a bit poor, because many installations will have no means of isolating the tail to a main RCD, so unless the circuit in question is RCBO-fed then bypassing the RCD would necessitate live working.For the purpose of testing, why not bypass/link out the rcd, do the test and then remove the links.
Aren't you a bit late for that?Before this thread decends into pointless gibberish:-
As a piece of generic advice that's a bit poor, because many installations will have no means of isolating the tail to a main RCD, so unless the circuit in question is RCBO-fed then bypassing the RCD would necessitate live working.For the purpose of testing, why not bypass/link out the rcd, do the test and then remove the links.
In that situation its's better to use a non-RCD-tripping EFLI tester, or else calculate EFLI having measured R1 and R2.
Could you point me to regulation to support that?Bypassing or linking across an RCD is completely unacceptable.
The Electrician on the ground needs to make that call, nobody else.There's the possibility of the incomer being live as already mentioned.
No, the test is to ensure that the EFLI is suffiiently low to provide prescibed disconnection times.The test is intended to confirm the connections are correct and properly made.
I disagree, disconnecting two wires, making a test, then reconnecting (correctly)the same two wires does not change the characteristics of the circuit at allUndoing them to remove the links would make the test invalid, since you have changed part of the circuit.
That would be an act of an incompetent person, that person should not be working with electrics.There is also the possibility of the links being left in place, making the RCD useless.
or remove devices sensitive to testingThe choices are either use a non-trip tester, or calculate Zs.
Wouldnt it be ZE + ((R1 + R2) x 1.2) to take into account the increase in temperature when the cables are running at operating temp?