Ep2002 wiring for a Hive dual

Sponsored Links
The only redundant wires here will be the ones in the cable going to the room stat, the red live link going to terminal 5 is made inside the Hive so that won't be needed, but the brown wire in terminal 5 will need to connect to L.

The wires in terminal C will need to remain connected together. It looks like the yellow wire in B is coming from your room stat, If that is the case then the black wire from B will need to be connected to the heating on terminal of the hive. The terminals on the Hive are not really designed for more than 2 wires so I'd recommend using a connector to join all the L wires and then run a single wire to the Hive.
 
B is neutral (Two black one blue)?

What one do i put C in too?
 
Last edited:
Sponsored Links
Wow, got it working mate. Connected original B and C together on hive and working!

thanks for the help.
 
um, spoke to soon, some weird behaviour going on with boiler it turns on when I press on the thermo button, but i need to reset the boiler.

im now knackered so will look tomorrow.
 