expansion vessel for combinaton boiler

Joined
15 Jan 2009
Messages
1
Reaction score
0
Location
Belfast
Country
United Kingdom
should the expansion vessel be filling with water, if not would this cause heating not to start? Would a new expansion vessel fix this problem?
 
Very possibly. The ch pressure will rise and be released through the pressure relief valve causing a low pressure situation when it cools down either failing to make the low water pressure switch or overheating and locking out.
 