hi guys
i have a 9.5kw shower fitted in my bathroom at the moment,was wondering if a standard single phase 100amp supply would be capable of feeding another 9.5kw shower in my en-suite ?

thanks
 
Sponsored Links
Not if they were both used at the same time, unless you turned off almost everything else in the property.

Two 9.5kW showers will draw around 80A when both elements are energised, leaving only 20A (officially) for cooking, lighting, TV, heating, 'fridging, and boiling a kettle. And that's ignoring the number of transformers left running while not charging your mobile phone / camera / iPod / laptop / bluetooth whatsits / toothbrush etc.

This idea of having two showers has been covered before on the forum - have you searched to see if any of the proposed solutions suits you?
 
Sponsored Links
And there are water pressure considerations as well...............
Not when merely determining "if a standard single phase 100amp supply would be capable of feeding another 9.5kw shower..." ;)
 
That's assuming it is actually a 100A fuse in the cutout....
 
The OP stated 100A.

Are you suggesting that he's got it wrong? :eek:
 
Although it probably says 100a its most likely a 60 or 80amp fuse internally.
 
Virtually all modern cutouts have 100A written on the outside of the fuse carrier, but in reality, there is often an 80A or sometimes even a 60A fuse in the carrier.
 
I wonder if it says 100A on the outside, but internally only has a 60A or 80A cut-out. :idea:
 