There has always been 2 there the second runs the fridge freezer, I have added a fused spur from the first socket on the right for a cooker hood. Dose the second socked need to be fused?That would be alright.
Note though that you have two sockets on the right hand side cable.
Sorry for all the questions dose it make any difference if its on a rcbo than a mcbEasiest thing to do would be to change the MCB for one of 20A then you can have as many sockets as you want.
So should look like thisIf there is more than one socket on the spur then a fused connector unit should before all of them.
So just need too pick up a 13 amp fused spur to fit before the socket?Yes, that would be alright.
No, RCBOs are the same in that respect.
Thanks for your help, just picked up a fused switchYes, but the cable is actually the spur.
Is it OK to use a 20A with 6mm cable?Easiest thing to do would be to change the MCB for one of 20A then you can have as many sockets as you want.