Fault finding with Fluke 116 DMM
8 Aug 2009
Sussex
Hello, I have installed an oil boiler to a property and wired up the controls according to the MI's.
When I turned on the permanent live to the boiler, the power light came on. When I put a demand on the boiler from the porgrammer, the burner demand light came on, but nothing else happened. No pump, no fan.
I set my Fluke to Auto Volts and upon tresting between the switched live input on the hot water and the boiler casing. The main RCD tripped.
Is there a fault with my wiring or should I use the DMM on a different setting? I've used plenty of DMM's in the past but I only bought this last week.
It appears to be a LoZ (Low Impedance) range, i.e. the meter takes more current to eliminate measuring a voltage caused by capacitive coupling etc. This is probably why the RCD tripped.
A high impedance range shouldn't cause the RCD to trip but can measure stray voltages which have no current behind them.
Yes, the auto volts position on the 116 is a low impedance setting. You will actually have to know if you're measuring AC or DC for this one!
You may also try not measuring between line and earth on a 30mA RCD protected circuit with a meter with 3 kΩ input impedance.
All of that is exactly what you would expect to happen.
As for the boiler not working - more likely to be some issue with the boiler itself, such as built in timer/programmer/other control not set correctly, or some installation/commissioning procedure has to be done first, or it has no fuel, no water, no pressure, etc.
If you've read and understood the manual, anyway. :)