Fire protection

Discussion in 'Building Regulations and Planning Permission' started by A_Novice, 17 Apr 2019.

  1. A_Novice

    A_Novice

    Joined:
    29 Dec 2017
    Messages:
    178
    Thanks Received:
    2
    Country:
    United Kingdom
    Hi guys,

    Quick and easy. For a timber frame first floor we need 6mm fire resistant board like Supalux to provide 30 mins protection.

    Does this board just go on the outside or does it also need to provide internal protection as well so used on the inside also?

    Our design at the moment looks like this.

    12.5mm plasterboard
    25mm insulation board
    150 x 47 studs with 90mm insulation between studs
    9mm osb
    6mm fire resistant board
    Breather membrane
    Battens
    Tiles

    Anything wrong with any of that?



    Thanks
     
  2. ^woody^

    ^woody^

    Joined:
    3 Sep 2006
    Messages:
    26,037
    Thanks Received:
    3,197
    Location:
    West Mids
    Country:
    United Kingdom
    The idea is to protect from external fire spread - this must be close to or on a boundary? The plasterboard provides the internal protection.

    I'd put the fire board on after the membrane, and ensure its a breathable board, I'm not sure if Supalux is. Or use the fire board as the sheathing instead of OSB and membrane

    Any why are you specifying a 150mm frame and only using 90mm of insulation? That air void is a risk. You can use a 89mm CLS for that insulation, or 150 Rockwool for a 150 frame.
     
  3. A_Novice

    A_Novice

    Joined:
    29 Dec 2017
    Messages:
    178
    Thanks Received:
    2
    Country:
    United Kingdom
    Thank you Woody.

    Yes it is within 1m of the boundary unfortunately

    The building notes I have specify 90mm celotex between the 150 studs.

    The builder starts in two weeks but I have found quite a few inconsistencies with the drawings and the building notes and also what the building inspector advises.

    E.g. drawings show 100mm studs for external timber, notes say 150mm. Building inspector approved the plans but later told me it must be 150mm studs and will tell the plan checkers to be more thorough next time.

    Building regs say CELOTEXFR for external walls. Building inspector says no it doesn't have to be after I told him it doesn't exist anymore.

    It all seems very wooly.

    I trust the builder I have chosen but can't help but feel nervous about all this.
     
  4. Notch7

    Notch7

    Joined:
    15 Sep 2017
    Messages:
    10,447
    Thanks Received:
    904
    Location:
    Sussex
    Country:
    United Kingdom
    Thats seems expensive at close to £100 / sheet.
     
  5. A_Novice

    A_Novice

    Joined:
    29 Dec 2017
    Messages:
    178
    Thanks Received:
    2
    Country:
    United Kingdom
    Have read enviroboards are a cheaper alternative. No idea how true that is though.
     
  6. John D v2.0

    John D v2.0

    Joined:
    26 Aug 2016
    Messages:
    5,609
    Thanks Received:
    750
    Country:
    United Kingdom
    edit: half hour protection from each side of the wall is alright, although after grenfell, you'd have thought they would tighten up the regs on that!
     
    Last edited: 18 Apr 2019
  7. A_Novice

    A_Novice

    Joined:
    29 Dec 2017
    Messages:
    178
    Thanks Received:
    2
    Country:
    United Kingdom
    Can you provide a link?

    Who regulates private building inspectors?
     
  8. John D v2.0

    John D v2.0

    Joined:
    26 Aug 2016
    Messages:
    5,609
    Thanks Received:
    750
    Country:
    United Kingdom
    ah you replied while I was looking it up, when I found it, the current regs do indeed say 30 minutes each side as long as window sizes are basically kept down, max 1m2. Perhaps the triple boarding was from a party wall. Anyway just disregard my comment!
     
  9. A_Novice

    A_Novice

    Joined:
    29 Dec 2017
    Messages:
    178
    Thanks Received:
    2
    Country:
    United Kingdom
    No probs. What provides the fire resistance on the inside? Or does one board like 6mm supalux provide enough.

    Just reread Woody's post and yes plasterboard from the inside
     
    Last edited: 18 Apr 2019
  10. John D v2.0

    John D v2.0

    Joined:
    26 Aug 2016
    Messages:
    5,609
    Thanks Received:
    750
    Country:
    United Kingdom
    inside would be plasterboard plus skim. You would only have to look closely at any windows and doors you fitted in that elevation.
     
  11. Leofric

    Leofric

    Joined:
    9 Nov 2018
    Messages:
    1,076
    Thanks Received:
    89
    Country:
    United Kingdom
    A vapour barrier on the warm side of the insulation is required and counterbattens under the horizontal battens . I would get whoever drew the plans to pull all this together now and co ordinate the drawings and building construction notes to Building Control's satisfaction before you start work on site.
     
  12. A_Novice

    A_Novice

    Joined:
    29 Dec 2017
    Messages:
    178
    Thanks Received:
    2
    Country:
    United Kingdom
    Thanks. Going to chase up the architect today.

    Having read a few bits over the weekend and taking on board the comments here what would be wrong with this.

    12.5mm plasterboard (foiled backed and taped to provide VCL)
    150 x 47 studs with 150mm rockwool insulation between studs
    fire resistant board (replacing OSB)
    Breather membrane
    Battens
    Tiles

    This way saves having the 25mm insulation boards and also combines the sheathing and fire resistant board into one.

    Does it provide enough insulation?

    Obviously there are a number of ways to do this.
    Read more: https://www.diynot.com/diy/threads/fire-protection.521660/#ixzz5ltoujUkx
     
  13. ^woody^

    ^woody^

    Joined:
    3 Sep 2006
    Messages:
    26,037
    Thanks Received:
    3,197
    Location:
    West Mids
    Country:
    United Kingdom
    Why isn't your designer doing all this instead of you having to alter the design?
     
    • Like Like x 1
  14. A_Novice

    A_Novice

    Joined:
    29 Dec 2017
    Messages:
    178
    Thanks Received:
    2
    Country:
    United Kingdom
    All sorted I hope.

    Building control are happy with

    Tiles
    Battens
    Membrane
    Fire resistant board
    OSB
    150 studs with 100mm insulation
    25mm insulation backed plasterboard taped at joints

    The builder and architect are happy with this. I did ask BC about not having OSB and just using the fire board as the sheathing but he wouldn't allow it as it is too brittle. (no doubt there is a product that combines the two)

    I also mentioned about the 50mm of cavity between the studs. All 3 said a small air gap is needed.

    I thought there were a few ways to skin this but it seems there are hundreds ha ha.
     
  15. ^woody^

    ^woody^

    Joined:
    3 Sep 2006
    Messages:
    26,037
    Thanks Received:
    3,197
    Location:
    West Mids
    Country:
    United Kingdom
    So, it seems you have a building inspector who is actually qualified in timber frame design and condensation risk analysis, and a designer who is not. I don't know if your builder should be happy or worried.
     