Evening all,

I'd be grateful if some of the more experienced members could cast an eye over my first draft of a wall design for a garden workshop.

The building is 7 m x 4 m externally. The strip foundations are already in at 1 m deep x 600 mm wide. That's probably overkill, but they're done now. I've laid one course of 300 mm trench blocks on top. I've attached a diagram of what I think I need to build from there up, and I'd appreciate it if you could point out any pitfalls or mistakes before I go further.

From my research, I understand the cavity below ground needs filling with a lean-mix concrete. This stops the soil outside and the hardcore inside pushing the two leaves together. I've also seen details where the top of the fill is sloped down towards the outer leaf, so any moisture in the cavity drains outwards. I've shown it that way in my drawing.

For the floor, other designs I've looked at suggest the usual build-up, from the bottom up, is:

- 100 mm Type 1 MOT, compacted
- 50 mm sand blinding
- DPM
- 100 mm concrete slab
- 100 mm Celotex (PIR) insulation
- Possibly a second DPM
- 50 mm screed

Any comments on the wall or floor details would be much appreciated.

Thanks in advance
 

Attachments

  • Wall 1.jpg
    Wall 1.jpg
    130.7 KB · Views: 18
I don’t think the cavity insulation would be celotex? Normally you’d have dritherm mineral wool batts full fill, or if using PIR you need interlocking boards and a clear gap between insulation and masonry. Also I’d carry the dritherm down to the lean fill sloped bit, and not have a cavity tray/dpm crossing the cavity. Not sure why you’d want that. Unless I’m out of date.

+ Screed is good, but if it’s a garden office a floating ply/chipboard floor on top of the floor PIR could also work and be easier…
 
Evening all,

I'd be grateful if some of the more experienced members could cast an eye over my first draft of a wall design for a garden workshop.

The building is 7 m x 4 m externally. The strip foundations are already in at 1 m deep x 600 mm wide. That's probably overkill, but they're done now. I've laid one course of 300 mm trench blocks on top. I've attached a diagram of what I think I need to build from there up, and I'd appreciate it if you could point out any pitfalls or mistakes before I go further.

From my research, I understand the cavity below ground needs filling with a lean-mix concrete. This stops the soil outside and the hardcore inside pushing the two leaves together. I've also seen details where the top of the fill is sloped down towards the outer leaf, so any moisture in the cavity drains outwards. I've shown it that way in my drawing.

For the floor, other designs I've looked at suggest the usual build-up, from the bottom up, is:

- 100 mm Type 1 MOT, compacted
- 50 mm sand blinding
- DPM
- 100 mm concrete slab
- 100 mm Celotex (PIR) insulation
- Possibly a second DPM
- 50 mm screed

Any comments on the wall or floor details would be much appreciated.

Thanks in advance
As said, stick the DPC's on the same level as the outer course and no need to breach the cavity unless you are installing a specific detail like Radon DPM for example.

Cavity walls - for simplicity and cost I'd go for say 100mm cavity batts. Brick outer and fibolite inner.
 
Full-fill PIR exists. It's the only way to get acceptable insulation with a 100mm cavity these days.

You need wall ties at the bottom of the PIR for it to sit on.

Are you really making the concrete 1000mm deep? If so the drawing's not to scale.

Your DPC detail will work IF your floor is 3 bricks higher than the ground. This is more than normal, usually it's 2 bricks higher. In which case you can't do what you've drawn. Personally I'd just use a standard 100mm DPC in each wall and nothing across the cavity, but I know the DPC across the cavity is the modern way. But to me it looks like a few mortar snots would easily turn into a damp bridge when sitting on it.

The concrete cavity fill can be up to 2 bricks below the floor. As you've drawn it, the wall is retaining the soil and floor beyond the height of the concrete.

Why one course of trench blocks? Use them or don't use them!
 
Thanks all for taking the time to respond. You've probably guessed I'm no builder. I fix air navigation aids (i.e. radar, radios, ILS) for a living, and this is my first attempt at a build. Most of what I've learned so far has come from research, YouTube videos and the advice and experience of people who know far more than I do, so I really appreciate you putting me straight where I've gone wrong. It's something I've wanted to do for many years, and only now do I have the time to take it on.

Having read your comments, I can see you're right about the Celotex. I'd also mistakenly thought Kingspan Thermawall was a full-fill board, but I now understand it's partial fill. I'd like to get as much insulation performance as is reasonable while I'm at the start of the build, so I've been looking at Kingspan Kooltherm K106, which is sold as full fill. From what I've read, it's normally 90mm in a 100mm cavity, leaving a small residual gap of around 10mm. Can it be used wall to wall, filling the cavity completely with no gap, or is the residual gap needed? And would you go for K106?

On the DPC, I'd drawn a single sloping one across both leaves because that's what I'd seen in a few YouTube videos, and I wondered if it was a new requirement. A separate DPC in each leaf, with the floor DPM lapped into the inner one, is certainly simpler than what I had.

I've attached a revised drawing based on your advice. The main changes are:
- concrete cavity fill brought up to 225mm below the DPC
- finished floor level at DPC level, with the DPM turned up and lapped into the inner leaf DPC
- floor build-up of 150mm hardcore, 50mm sand blinding, DPM, 100mm slab, 100mm insulation, separation layer and 65mm screed

Again, very much appreciate the advice.
 

Attachments

  • Wall second attempt..png
    Wall second attempt..png
    353.3 KB · Views: 3
Thanks all for taking the time to respond. You've probably guessed I'm no builder. I fix air navigation aids (i.e. radar, radios, ILS) for a living, and this is my first attempt at a build. Most of what I've learned so far has come from research, YouTube videos and the advice and experience of people who know far more than I do, so I really appreciate you putting me straight where I've gone wrong. It's something I've wanted to do for many years, and only now do I have the time to take it on.

Having read your comments, I can see you're right about the Celotex. I'd also mistakenly thought Kingspan Thermawall was a full-fill board, but I now understand it's partial fill. I'd like to get as much insulation performance as is reasonable while I'm at the start of the build, so I've been looking at Kingspan Kooltherm K106, which is sold as full fill. From what I've read, it's normally 90mm in a 100mm cavity, leaving a small residual gap of around 10mm. Can it be used wall to wall, filling the cavity completely with no gap, or is the residual gap needed? And would you go for K106?

On the DPC, I'd drawn a single sloping one across both leaves because that's what I'd seen in a few YouTube videos, and I wondered if it was a new requirement. A separate DPC in each leaf, with the floor DPM lapped into the inner one, is certainly simpler than what I had.

I've attached a revised drawing based on your advice. The main changes are:
- concrete cavity fill brought up to 225mm below the DPC
- finished floor level at DPC level, with the DPM turned up and lapped into the inner leaf DPC
- floor build-up of 150mm hardcore, 50mm sand blinding, DPM, 100mm slab, 100mm insulation, separation layer and 65mm screed

Again, very much appreciate the advice.
If you want to achieve 0.18 W/m²K for the walls, whilst maintaining only a 100mm cavity, then you need to go for the rebated 'full fill' PIR stuff. It's expensive to buy and expensive and difficult to fit. Some brickies will walk away from these jobs. Yes it is 90mm with a nominal 10mm fitting gap. the 10mm gap is needed for masonry discrepancies and is not regarded as a gap at all in the true sense.

We use it on a lot of jobs these days, but it's not our favourite part of the build. :mad:

Personally I'd go for 100mm fibreglass cavity batts for a workshop, but it's up to you.
 
Thanks for the advice noseall. tbh, the build is going to be partly gym, workshop and somewhere to have a drink so I want to do the best I can first time. I don't mind a bit of pain for long term gain. Again, cheers for the help.
 