fused spur under bath

Joined
8 Oct 2003
Messages
7,096
Reaction score
553
Location
Bristol
Country
United Kingdom
I presume underneath the bath is a prohibited zone but what if the spur is in a wooden cupboard with a door under the bath....still prohibited?, standard 240v. Just needing to advise someone else.
 
Sponsored Links
If you have a bath panel which is only removable with the use of a tool then under the bath is not a restricted zone so a spur is fine.

I presume you mean a Fused Connection Unit; the cable is the spur.
 
A tool such as a screwdriver?, Its the power switch to the boiler in a little wooden cupboard under the bath
 
Yes, screwdriver counts.

Silly place for the Boiler switch but not against any regulation, as such.
 
Sponsored Links
Where is the boiler? Under the bath is a stupid place to to have the boiler switch, it should be accessible and within reach of the boiler.
 