Hi all,

Planning to upgrade the electrical supply to my detached garage at some point in the future and trying to establish how a sparky would normally approach this before getting quotes. Currently the garage is supplied from the kitchen cooker circuit via SWA buried under the patio. It is rough to say the least. I'd like to replace this with a dedicated submain.

The proposed setup is fairly straightforward:
  • 100A supply, TN-C-S/PME.
  • Existing Henley blocks with a spare connection.
  • Approx. 16m of 16mm2 3-core SWA to the garage, mostly underground ducting with a drawstring and that's part of this job that I'll be doing myself.
  • I think a 63A switch-fuse at the supply end, subject to what sparky says.
  • New garage CU with 100A mains switch, SPD and individual RCBOs when I tidy this up. Again, its an inherited total mess.
  • Existing 3.6kW grid-tied solar inverter would eventually connect to the garage CU on its own protected circuit instead of the current Proteus CU.
My main question is about where and how you'd normally install the switch-fuse. There's approximately 200 × 200mm of usable space in the bottom-right corner of my external meter cabinet as per first pic.

I've been looking at two possibilities:

Option 1: One of those small plastic domestic switch-fuses (Contactum/FuseBox type), mounted inside the meter cabinet, with the SWA properly terminated separately using an appropriate gland and earthing arrangement, similarly to the attached pic.

Option 2: A small metal-clad switch-fuse, such as the LIVE MCFS100/3F (225 × 115 × 82mm), mounted vertically on the inside right-hand wall of the meter cabinet, assuming adequate clearance. This would potentially allow the SWA to be glanded directly into the metal enclosure.

I've seen examples of both arrangements in other domestic meter cabinets, but appreciate that doesn't necessarily mean either is acceptable in mine.
The third option would be to retain an existing external Proteus solar CU and use a suitably rated MCB to protect the submain, although the whole idea behind it is to eliminate that enclosure if possible so I wouldn't have wires and random boxes all over the house.

What would you normally do in this situation? Is mounting a compact switch-fuse inside a domestic external meter cabinet acceptable practice, assuming there's sufficient clearance? Would you generally favour the metal-clad switch-fuse with direct SWA termination over a compact plastic unit with a separate gland arrangement?

Not looking for instructions on working with meter tails or DNO equipment. Just trying to understand what a professional installer would consider the neatest, most sensible solution so I can specify the job properly when requesting quotes.

Photos attached showing my existing cabinet and an example installations(I'm aware its a messy pic but shows how a sparky installed it!).
 

Attachments

  • meterbox.jpg
    meterbox.jpg
    663.5 KB · Views: 37
  • normalswitchedfuse.jpeg
    normalswitchedfuse.jpeg
    765.5 KB · Views: 36
  • compactswitchefuse.png
    compactswitchefuse.png
    389.7 KB · Views: 37
Meter cabinet is for DNO equipment. Stay clear of it. Your electrical contractor will design the installation - it's not for you to do.
My "electrical contractor" "designed" the abomination in the picture, which is that Proteus CU, without the slightest care in the world, I'd rather be more specific this time around when talking to them so I could avoid random boxes and clipped cables all around the house if possible, that's all
I know meter cabinet is for DNO equipment and you can't have e.g. consumer units in there but I've seen conflicting info re switched fuses and the attached pics show sparky designed jobs.
I've designed service placement at home as part of this for the loft inverter and future heat pump already, hence why planning the earthwork for this for next year now too.
 
most dnos will throw a fit if they see customer switchgear squeezed into their meter cabinet mate, technically you're only meant to have their cut-out and meter in there. best way any sparky will quote is popping a 63a or 80a metalclad switch-fuse just inside the property right behind the meter box, then glanding your 16mm swa straight into that before taking it out through the cavity. keeps the dno happy and gives you a solid metal enclosure for the swa brass gland without worrying about plastic boxes cracking under tension.
 
a professional installer would consider the neatest, most sensible solution
The switchgear / consumer unit / whatever else goes inside the property.
Not outside, not in the meter cabinet.

All 3 of those photos are examples of where incompetent box slingers have had a go and then rode off into the sunset on their 3 legged horse.
 
Haha! Bit harsh on your fellow electricians, isn't it? :D Three incompetent box slingers and not a single four legged horse between them? Sounds like the entire industry is in desperate need of better training, stricter entry requirements and a competent farrier.
 
Three installs, non perfect, as to which is yours not a clue, so in general terms.
1) As said the meter board is for DNO use only.
2) Today looking at RCD protection and SPD so the Wylex board needs replacing.
3) Out side consumer units may be technically allowed, but really it needs to be at least under cover.
4) The DNO supply can be 60, 80, or 100 amps, any thing directly connected to the DNO supply today really needs rating at 100 amps.
4B) I you also have solar panels, you may need a second fuse or over a 100 amps in some places to work with combined solar and DNO supply.
5) Any work will need to be registered, at least it does here in Wales, and no one will want to put their name on others peoples work.
So you select an electrician and see what he will agree to do.
 
The switchgear / consumer unit / whatever else goes inside the property.
Not outside, not in the meter cabinet.

All 3 of those photos are examples of where incompetent box slingers have had a go and then rode off into the sunset on their 3 legged horse.
But what do you really mean? :whistle:
 
Last edited:
I'm confused - you say you're currently fed from the kitchen cooker switch - what's the proteus box for?
It might be best practice to install switchgear indoors where possible but I'd hardly call that install an abomination - it's clearly an outdoor rated box and looks reasonably tidy.

If that's for something else, is there any reason you can't use one of the spare ways in the proteus board?
 
I'm confused - you say you're currently fed from the kitchen cooker switch - what's the proteus box for?
It might be best practice to install switchgear indoors where possible but I'd hardly call that install an abomination - it's clearly an outdoor rated box and looks reasonably tidy.

If that's for something else, is there any reason you can't use one of the spare ways in the proteus board?
Proteus box is for the solar inverter, its not that its untidy, its just at the front of the house and looks fugly. I now have a "service corridor" inside the house, along the main soil stack so can route the cable through there and the outside wall and into the garage when I get the ducting buried under the driveway sometime next year which will mean there wont be any ugly cables clipped anywhere and I could get rid of the Proteus then, and move the inverter rcbo and the generation meter to the garage, just need to figure out upstream cable protection without ugly arse cables and boxes everywhere.
I've just bricked up the garage door so future me can also get a heat pump there so kinda makes sense to move these to the garage submain, its just going to be much tidier that way.
I'll do the earthwork and have a sparky connect it all when the ducting is ready(still need to figure that bit out with the access points, etc).
 
weatherproof
Only 'weatherproof' with the cover closed.

Open it and whatever is inside is exposed to the external environment with all the dirt and humidity that exists.
Even with it closed, they will be subject to massive temperature variations which will lead to condensation.

Most MCBs and other similar devices used in domestic consumer units are rated PD2, for use indoors.
While PD3 and PD4 rated devices can be had, they are intended for use in industrial distribution boards.
 