Garage submain - compact switch-fuse inside meter cabinet or metal-clad unit?

Proteus box is for the solar inverter, its not that its untidy, its just at the front of the house and looks fugly. I now have a "service corridor" inside the house, along the main soil stack so can route the cable through there and the outside wall and into the garage when I get the ducting buried under the driveway sometime next year which will mean there wont be any ugly cables clipped anywhere and I could get rid of the Proteus then, and move the inverter rcbo and the generation meter to the garage, just need to figure out upstream cable protection without ugly arse cables and boxes everywhere.
I've just bricked up the garage door so future me can also get a heat pump there so kinda makes sense to move these to the garage submain, its just going to be much tidier that way.
I'll do the earthwork and have a sparky connect it all when the ducting is ready(still need to figure that bit out with the access points, etc).
Fair enough, you're unlikely to need a 16mm cable for a garage unless you're planning on a hot tub out there.

Only 'weatherproof' with the cover closed.

Open it and whatever is inside is exposed to the external environment with all the dirt and humidity that exists.
Even with it closed, they will be subject to massive temperature variations which will lead to condensation.

Most MCBs and other similar devices used in domestic consumer units are rated PD2, for use indoors.
While PD3 and PD4 rated devices can be had, they are intended for use in industrial distribution boards.
These units are sold prepopulated with consumer grade mcbs/rcds.

I'd never heard about pollution degree, on googling this is what professional electrician has to say -

circuit- breakers to BS EN 60898 must be used in domestic settings.

While this standard is based on PD2 conditions (where only non-conductive pollution occurs), it does acknowledge that temporary conductivity, such as that caused by condensation, may occasionally be expected.

Therefore, installers should not be concerned about using BS EN 60898 circuit-breakers in outdoor enclosures, provided the manufacturer has tested and validated the assembly arrangement as suitable for such use.
 
There's an infrared heater in the garage(its a man cave), another outdoor heater for the pergola from the outdoor socket supplied from the garage), a few sockets and lights, nothing too exciting. But add to that my existing solar inverter, which I want to relocate there, a future heat pump (as it's pretty much the only suitable place for one), and potentially another AC coupled inverter for larger battery storage, and 16mm2 starts looking like a sensible bit of future proofing. I'd rather overspec the cable now than dig up the driveway or cable again in a few years.
 
I think it needs a site inspection to work out what can be done. I know my own home has some limitations, like a 60 amp DNO fuse, which if up-graded, would also mean adding other fuses or overloads as consumer unit only rated 100 amps, so with solar and battery, it could exceed that if the DNO fuse was bigger.

The patio heater rings alarm bells, as so many are class I, meaning potential earthing problems if used outside.

But one can go round and round in circles, as there may be no problem, you could be on a TT earthing system, and a split phase supply for all we know, although unlikely, so really a forum is not the place to ask.

I have myself looked at heat pumps, but this house has only one open grate where I could light a fire if we have a power cut, I well remember 1978 with a labour government in power, and a freezing house, don't want a repeat of that, so unless I also have a back-up generator to run the heat pump, it's a non starter.
 
Fine - you carry on voting on the basis of the political landscape half a century ago, that will make sense.

Don't vote Tory though - they did much deeper and permanent damage than the WoD caused, and it's only right that they should be judged in perpetuity for what Thatcher did. Or maybe for what Lord Liverpool did in the 1810's.
 
I think it needs a site inspection to work out what can be done. I know my own home has some limitations, like a 60 amp DNO fuse, which if up-graded, would also mean adding other fuses or overloads as consumer unit only rated 100 amps, so with solar and battery, it could exceed that if the DNO fuse was bigger.

The patio heater rings alarm bells, as so many are class I, meaning potential earthing problems if used outside.

But one can go round and round in circles, as there may be no problem, you could be on a TT earthing system, and a split phase supply for all we know, although unlikely, so really a forum is not the place to ask.

I have myself looked at heat pumps, but this house has only one open grate where I could light a fire if we have a power cut, I well remember 1978 with a labour government in power, and a freezing house, don't want a repeat of that, so unless I also have a back-up generator to run the heat pump, it's a non starter.
Cheers, appreciate that a site inspection might be needed before anything gets installed or even agreed. I'm not expecting anyone to sign off the installation from a forum photo, just trying to understand what arrangements electricians would normally consider and therefore what to ask them.
For clarity, the supply is confirmed 100A single-phase TN-C-S/PME, so we can probably rule out the mystery split phase TT installation :D

The outdoor heater is a normal Class I appliance on an RCD protected circuit. Nothing inherently wrong with class I equipment for outdoor use as far as I'm aware, it is properly installed and earthed. I'm also aware of the potential issues with multiple generation sources and CU ratings, which is partly why I'm planning all this well in advance rather than just throwing another inverter at the installation.

As for the heat pump, I certainly hadn't anticipated my garage submain question taking us all the way back to the winter of 1978 and the Labour government, but here we are :ROFLMAO:
Anyway, the original question was really just whether a compact switch fuse inside the meter cabinet or a separate metal clad unit would be the preferred approach. I'm going to have to find a local sparky, see what they say and how I could best bury the cable in the wall and then underground all the way to the garage(currently looking at some beautiful Uponor Ecoflex options!). Meter box sits on the vestibule wall and the house CU is on the other end of that wall. It is a modern Wylex unit with all bells and whistles(SPD and AFDDs). I'm not against having a switched fuse in the vestibule if a sparky can hide the SWA in the wall.
 