Garage submain - compact switch-fuse inside meter cabinet or metal-clad unit?

Nope, it's a late 90s house built on a concrete slab.

I'm not against having the switch fuse indoors, and initially thought that might actually be the tidiest option. The problem is getting the cables to it without turning my vestibule into a miniature electrical substation :ROFLMAO:

The meter cabinet is outside, directly underneath that window, so the tails could come through the wall, run left and then up to a switch fuse mounted on the opposite side of the window from the existing CU. That's straightforward enough.

The awkward part is the 16mm2 SWA leaving the switch fuse. Ideally, I'd want it concealed in the wall, running down and left underneath the doorway before entering the underground ducting towards the garage. Unfortunately, most of the compact metal switch-fuses I've found only have top/bottom cable entries, and terminating SWA neatly from behind one of those doesn't look particularly straightforward. Recessing the entire enclosure seems a bit excessive too and probably not something any sparky would be happy with!

Another possibility is retaining the existing outdoor Proteus CU and fitting a suitable DIN mounted fuse switch disconnector, rather than an MCB. I've been looking at some Wöhner units which might make that quite straightforward, assuming they're compatible.
That would certainly be the easiest option electrically, although it means keeping the ugly box on the front of the house, which I was really hoping to eliminate.

I'll have to investigate the options a bit more. I'd much rather spend some time planning it now than end up with cables and boxes decorating every available wall, I really don't like how difficult it seems to be to figure out a tidy install with no visible wires running everywhere! :LOL:
 

Attachments

  • vestibule.jpg
    vestibule.jpg
    246.4 KB · Views: 10
Why 16mm²?

Have you worked out what loads are going to be used?

I know my house is much older (1960), but its supply cable has the imperial cable size 7/.052, which is the equivalent of ~ 9.4mm² and that's running the whole house via a 100A fuse.
 
I know the cable sizing rules are different for DNOs, before anybody says anything.

But even so, 16mm² is a serious CSA.

Is the run a long one?
 
Why 16mm²?

Have you worked out what loads are going to be used?

I know my house is much older (1960), but its supply cable has the imperial cable size 7/.052, which is the equivalent of ~ 9.4mm² and that's running the whole house via a 100A fuse.
Yes, roughly. The garage itself will have around 3kW of potential loads, including infrared heaters, sockets and lighting. Then there's a planned small air to water heat pump, my existing 3.6kW Solis inverter which I want to relocate there, and potentially another, lets say 5kW AC coupled battery inverter in the future. The EV charger will be supplied separately from the house and I've made provisions for that already.

I'm planning a 60-63A switch fuse and approximately 16m of 3 core SWA, mostly buried in ducting. 16mm2 isn't necessarily because I need that much capacity today, but because I'm designing it for the next 20 or 30 years rather than just the current garage loads. It gives me some headroom for future equipment, voltage drop and installation derating. May as well do it once and do it good and not look into it again.

I appreciate your old supply cable has survived perfectly well, but I imagine a 1960s DNO service cable and a new underground submain aren't necessarily a like for like comparison :D Besides, I'd much rather spend a little extra on copper now than dig up the driveway again in five or ten years!
 
I was thinking about just using a breaker in your CU rather than a dedicated switch, youd probably need to have a JB on the other side of the wall though and drill straight out.
Other than that, a small board below the meter box or bodging something into the box are your only real options.
It's worth pointing out that the solar can be discounted as a load, it can't add to the supply cable current only reduce it.
 
The general sparky consensus seems to favour switched fuse over MCB to protect upstream cable because of selectivity. I do like the idea of one of these recessed DIN boxes with a wohner din switched fuse if it was to be installed inside the vestibule. I think that could be doable and look sensible.
Bodging something into the meter box is definitely also an option. Lots of sparkies recommending Eaton MEM Memera 800KMF switched fuse in the past, even on this forum and definitely inside the meter box so I'll definitely be asking about that even if it isn't exactly right :LOL:

My Solis can export approx 16A back towards the house. A future 5kW battery inverter could add another ~22 A, potentially giving 38A of reverse current through the submain, that's why I'm going with 60A+ and 16mm2 because that will make it easy to upgrade inverters if I ever wanted to.
 

Attachments

  • Wohner-FOT_ART_STA_31308_IN.png
    Wohner-FOT_ART_STA_31308_IN.png
    363.5 KB · Views: 0
  • Live-Electrical-FMC04-4-Module-Flush-Mounted-Metal-Enclosure.webp
    Live-Electrical-FMC04-4-Module-Flush-Mounted-Metal-Enclosure.webp
    8.2 KB · Views: 0