I've just checked the gas rate on my 12month old wall mounted fire and it works out at 5.75kw it should be 5.1kw, i doubt the injectors are worn, so why is this or is it to close to the MI figures that there is no need to take any further action.


at what difference +/- do you gas people take further action?
 
Corgi say +10%/-20%
So it's obviously about to EXPLODE :shock:
 
Gross

The MI figures are gross and i worked out the gas rate without dividing by 1.1.
 
bster said:
I've just checked the gas rate on my 12month old wall mounted fire and it works out at 5.75kw it should be 5.1kw, i doubt the injectors are worn, so why is this or is it to close to the MI figures that there is no need to take any further action.


at what difference +/- do you gas people take further action?

it is + or - 5%
 
22mb, i'll redo the gas rate three times and take the average.
 
Araldite your useless RIDDOR pad to the side of the fire so you can't quite turn the knob up full...
 
so its fine :D

err.. i just worked out that it is +12% so its not fine :cry:
 
The rated burner pressure is 20mb +/-1 and is running bang on 21mb at max rate.
 
bster said:
The rated burner pressure is 20mb +/-1 and is running bang on 21mb at max rate.

cant see any probs here if your still a bit picky about it go and buy a new injector, could be that its slightly out
 