• Looking for a smarter way to manage your heating this winter? We’ve been testing the new Aqara Radiator Thermostat W600 to see how quiet, accurate and easy it is to use around the home. Click here read our review.

Glow worm Flexicom 30CX Error code F4

Joined
5 Jan 2010
Messages
3
Reaction score
0
Location
Derby
Country
United Kingdom
Hi all,

My wife is having problems at home with the combi boiler.

There is a F4 message on the display and i'm wondering if any of you good people know what it is and if there is a simple fix?

Cheers in advance.
 
Just to update anyone who cares, it seems the cold snap is freezing the condensation pvc pipe which is causing the F4 error message.
 
arisomar,

I think I have the same issue. Did you manage to fix it? How?

Thank! :)

1). Warn the downstairs neighbour NOT to leave via his patio door;

2). Boiled a pan of water;

3). Opened my window;

4). Threw said boiling water at the pipe!

5). Contacted landlord to have the pipe lagged :)
 
Lagging a condensate or any other pipe will delay freezing but when its very cold and particularly when there is a strong wind then pipes will still freeze.

Thats why an internal condensate connection is by far the better way to install boilers.

Tony
 

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top