Glow worm flexicom sx boiler tripping out after a few hours

Joined
17 Mar 2011
Messages
1
Reaction score
0
Location
Essex
Country
United Kingdom
Just had a flexicom sx gloworm boiler installed and it's trippin the rcbo every few hours had the motorised valve On the tank changed as this was reported as the fault but It still continues. Tester has said circuit is all fine and gloworm been out and said the boiler is fine yet the problem persists any ideas?[/list]
 
Sponsored Links
I would disconnect all external controls and if it persists then its obviously the boiler.

Have you checked the tripping current of the RCBO ?

Have you checked the house leakage current?

Tony
 

DIYnot Local

Staff member