A friend of mine has just moved house.
The new property has a Glow Worm Fuel Saver MkII boiler.

Can a room thermostat be added to this boiler/system ?
 
Sponsored Links
What other controls is there . ie 2 motorised valves or one 3 port
 
No it hasn't got a motorised valve.
Just a manual 3 position port.

Next question will be can a motorised valve be fitted?
 
Sponsored Links
Now thats the reason i asked what existing controls.
You will need either an S plan pack or a Y plan pack .
That will include roomstat, cylinder stat and a programmer so HW and CH can be on seperatley or together,
They come with appropriate wiring diagrams
You will also need the boiler wiring instructions as it has to have a switched live and a permenant live as it has a pump over run on it.
And if the boiler has previously replaced an old servowarm system (they used manual valves) the pipework may need altered and pump moving etc
 
Thanks for the info.

The million dollar question is: Approx how much will be the cost??
 