gloworm24cxi

Joined
16 Jun 2005
Messages
10
Reaction score
0
Location
Leicestershire
Country
United Kingdom
hi all,fitted a bathroom today everything good towel rail also switched off boiler gloworm cxi condensating i think. my problem is when put back on f5 cape flashing and it wouldn t let me fill the filling loop to more than 0.8bar anyone have any answers or should i leave it to british gas think air in system maybe pump want bleeding
 
you need to find the overheat stat inside the grey metal cover on the top left of the boiler and press the little button in the middle of the stat, then it will let the system run so you can bleed out some more air
 
worked atreat ollski thanks pal, great help just started working in bathroom fitting so ,great advice cheers steve
 