Glowworm 30ci pressure keeps rising

Joined
19 Sep 2007
Messages
2
Reaction score
0
Location
Kent
Country
United Kingdom
Hi can anyone help with this, my boiler (glowworm 30ci) keeps dripping from i think its called the pressure zone, its not constant. and the pressure keeps rising everytime we use the hot water or heating i think the filling valve is to blame but can anyone confirm this for me many thanks
 
Sponsored Links
Is the filling loop turned off properly? Disconnect it and see if pressure still keeps rising.
 
thanks for your reply the filling valve was broken inside and so was not shuting off properly, fixed for now. but i'll have to get a new one on order tomorrow thanks for your help
 