Hi all
Here's one for you. Called to the above boiler, wasn't firing. On inspection, the reset button was lit, so reset it. Fan then cut out. Took cover off, water seemed to be coming from the baffle cover, looked above it and spotted that the Auto air vent was open so close it. Dried the water up. Customer then tells me that the trouble all started when the bathroom light tripped. Looked at the electrics - the large rectangle condesate trap was leaking directly onto the 11 pin relay, there was also long term rusting noted on the control panel. Dried everything off. No oil coming through so stuck a new solenoid on, still nothing, new control box - bingo she lights.
Customer turned down the heating from the room stat, 11 pin relays smokes like a chimney, so I switched it off and removed the relay, pin 1 and the adjactent (not 2, the other side) are heavily charred. So I got a new one. Fitted it boiler lights - boiler does not switch off!!!!! So tried the control panel temp control, 11 pin relay starts to smoke!!
Whats going on? I cannot find any spares for this boiler at all the MI's are not good, the fault diagnosis is a joke, mentions part replacement but not what the part number. Please help, customer has two small kiddies and its getting colder. All ideas welcome.
Again, thanks in advance
Here's one for you. Called to the above boiler, wasn't firing. On inspection, the reset button was lit, so reset it. Fan then cut out. Took cover off, water seemed to be coming from the baffle cover, looked above it and spotted that the Auto air vent was open so close it. Dried the water up. Customer then tells me that the trouble all started when the bathroom light tripped. Looked at the electrics - the large rectangle condesate trap was leaking directly onto the 11 pin relay, there was also long term rusting noted on the control panel. Dried everything off. No oil coming through so stuck a new solenoid on, still nothing, new control box - bingo she lights.
Customer turned down the heating from the room stat, 11 pin relays smokes like a chimney, so I switched it off and removed the relay, pin 1 and the adjactent (not 2, the other side) are heavily charred. So I got a new one. Fitted it boiler lights - boiler does not switch off!!!!! So tried the control panel temp control, 11 pin relay starts to smoke!!
Whats going on? I cannot find any spares for this boiler at all the MI's are not good, the fault diagnosis is a joke, mentions part replacement but not what the part number. Please help, customer has two small kiddies and its getting colder. All ideas welcome.
Again, thanks in advance