A plumbing friend of mine has been asked to look at installing a Grant 36kW Combi in a system with 12 double rads and asked me to have a look at the MIs and give my opinion of whether the installed 14L EV is big enough to accomodate these 12 rads.
I don't know the rad sizes but probably safe enough to all0w say 10L/rad? for a total of 120L.
The stated boiler+store contents are 53.5L so a total system vol of 175L.
The Mis state for this combi boiler, precharge&filling pressures of 0.5bar sufficient for system contents of only 148L.
My calcs, below show that this results in a final pressure of only 0.95bar, the PRV on all the Grants is set to 2.5bar so I can't see any reason why a final pressure of 2.0bar isn't perfectly acceptable.
Again, by my calcs, a total system contents of 322L, 269L to rads will still only result in a final pressure of 2bar.
IMO, the filling pressure should be 0.25/0.5bar higher than the precharge pressure to allow for any tiny leakages or collapsing air bubbles without the need for constant top ups, precharge/filling pressures of 0.5bar/1.0bar, water reserve 3.5L, would result in slightly higher final pressure of 2.13bar with 120L of rads+pipework and precharge/filling pressures of 0.75bar/1.0bar, water reserve 1.75L, will accomodate 135L of rads+pipework at a final pressure of 2bar.
I don't know the rad sizes but probably safe enough to all0w say 10L/rad? for a total of 120L.
The stated boiler+store contents are 53.5L so a total system vol of 175L.
The Mis state for this combi boiler, precharge&filling pressures of 0.5bar sufficient for system contents of only 148L.
My calcs, below show that this results in a final pressure of only 0.95bar, the PRV on all the Grants is set to 2.5bar so I can't see any reason why a final pressure of 2.0bar isn't perfectly acceptable.
Again, by my calcs, a total system contents of 322L, 269L to rads will still only result in a final pressure of 2bar.
IMO, the filling pressure should be 0.25/0.5bar higher than the precharge pressure to allow for any tiny leakages or collapsing air bubbles without the need for constant top ups, precharge/filling pressures of 0.5bar/1.0bar, water reserve 3.5L, would result in slightly higher final pressure of 2.13bar with 120L of rads+pipework and precharge/filling pressures of 0.75bar/1.0bar, water reserve 1.75L, will accomodate 135L of rads+pipework at a final pressure of 2bar.
| Grant 36kW Combi EV sizing & pressures. (Recommended) | ||||
| Precharge/Filling pressures 0.5bar/0.5bar | ||||
| System Capacity (from Grant Mis) | 148.00 | Litres | ||
| Boiler+store | 53.50 | Litres | ||
| Net to rads | 94.50 | Litres | ||
| Final Pressure | 0.95 | Bar | ||
| Grant 36kW Combi EV sizing & pressures | ||||
| Precharge/Filling pressures 0.5bar/0.5bar | ||||
| System Capacity | 322.00 | Litres | ||
| Boiler+store | 53.50 | Litres | ||
| Net to rads | 268.50 | Litres | ||
| Final Pressure | 2.01 | Bar | ||
| Grant 36kW Combi EV sizing & pressures | ||||
| Precharge/Filling pressures 1.0bar/1.0bar | ||||
| System Capacity | 215.00 | Litres | ||
| Boiler+store | 53.50 | Litres | ||
| Net to rads | 161.50 | Litres | ||
| Final Pressure | 2.01 | Bar | ||
| Grant 36kW Combi EV sizing & pressures | ||||
| Precharge/Filling pressures 0.5bar/1.0bar | ||||
| System Capacity | 162.00 | Litres | ||
| Boiler+store | 53.50 | Litres | ||
| Net to rads | 108.50 | Litres | ||
| Final Pressure | 2.01 | Bar | ||
| Grant 36kW Combi EV sizing & pressures | ||||
| Precharge/Filling pressures 0.75bar/1.0bar | ||||
| System Capacity | 188.00 | Litres | ||
| Boiler+store | 53.50 | Litres | ||
| Net to rads | 134.50 | Litres | ||
| Final Pressure | 2.01 | Bar |