Calling all Grant experts please!
Just moved to a house with a Grant Vortex Condensing Combi 26 (2006) with full underfloor heating.
The plot so far:
All was happy until cranking the heating up to 27 degrees, next day no hot water.
Figured out if the heating was calling for heat the hot water would work.
First thoughts were DHW plate heat exchanger or blend valve.
Auto vent valve replaced as seized (some black deposits came out), removed blend valve which was quite clean and put back on.
Hot water working again (weird), however now no heating if water store switched on and DHW pump constantly running.
If I turn off water store, DHW pump stopped immediately and CH pump starts.
Tested flow switch, pressure switch and both thermistors, all ok.
Now thinking PCB or back to my first though DHW plate heat exchanger maybe flow issue?
Please help as I am now at a loss.....
Just moved to a house with a Grant Vortex Condensing Combi 26 (2006) with full underfloor heating.
The plot so far:
All was happy until cranking the heating up to 27 degrees, next day no hot water.
Figured out if the heating was calling for heat the hot water would work.
First thoughts were DHW plate heat exchanger or blend valve.
Auto vent valve replaced as seized (some black deposits came out), removed blend valve which was quite clean and put back on.
Hot water working again (weird), however now no heating if water store switched on and DHW pump constantly running.
If I turn off water store, DHW pump stopped immediately and CH pump starts.
Tested flow switch, pressure switch and both thermistors, all ok.
Now thinking PCB or back to my first though DHW plate heat exchanger maybe flow issue?
Please help as I am now at a loss.....