Grundfos Alpha+ pump running continuously

Discussion in 'Plumbing and Central Heating' started by soulcake, 4 Nov 2021.

  1. soulcake

    soulcake

    Joined:
    4 Nov 2021
    Messages:
    5
    Thanks Received:
    1
    Country:
    United Kingdom
    I’m currently experiencing an issue with a Grundfos Alpha+ pump running continuously in my unvented heating system and would appreciate any advice. It continues to run when both the heating and hot water are turned off. When there is demand, the radiators do get hot as expected. Both zone valves appear to work, at least there is resistance when there is no demand and they activate when there is. Resetting or turning the boiler off doesn’t stop the pump either, only turning it off at the wall socket does. Any suggestions?

    The boiler is an Ideal Icos HE12 and it displays ‘C’ with the burner light flashing while the pump runs (with both heating and hot water off).

    The earliest I can get someone to look at it is early next week unfortunately, but if there are things I could check in the meantime that’d be great.
     

    Attached Files:

  2. Sponsored Links
  3. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    23,966
    Thanks Received:
    10,066
    Location:
    Livingston
    Country:
    United Kingdom
    which boiler do you have ? sorry just seen you had said , the C and burner light flashing means the boiler has reached the set temperature, or there is a blockage, sounds like you have a sticking micro-switch on one of the zone valves
     
    Last edited: 4 Nov 2021
    • Thanks Thanks x 1
  4. soulcake

    soulcake

    Joined:
    4 Nov 2021
    Messages:
    5
    Thanks Received:
    1
    Country:
    United Kingdom
    Hi, it’s an Ideal Icos HE12 boiler.
     
  5. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    23,966
    Thanks Received:
    10,066
    Location:
    Livingston
    Country:
    United Kingdom
    yes I noticed did you see my reply above
     
  6. soulcake

    soulcake

    Joined:
    4 Nov 2021
    Messages:
    5
    Thanks Received:
    1
    Country:
    United Kingdom
    Thanks, is it possible to check the micro-switch easily or best left to someone qualified?
     
  7. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    23,966
    Thanks Received:
    10,066
    Location:
    Livingston
    Country:
    United Kingdom
    easily checked , do you have and know how to use a multi meter ?
     
  8. soulcake

    soulcake

    Joined:
    4 Nov 2021
    Messages:
    5
    Thanks Received:
    1
    Country:
    United Kingdom
    Sorry for the slow reply, the heating system isn’t the only thing that’s packed in today. Yes I have access to a multimeter and can use to troubleshoot.
     
  9. Sponsored Links
  10. CBW

    CBW

    Joined:
    26 Sep 2019
    Messages:
    9,652
    Thanks Received:
    2,638
    Location:
    North
    Country:
    United Kingdom
    Edited - as inaccurate information
     
    Last edited: 4 Nov 2021
  11. stem

    stem

    Joined:
    20 Jul 2005
    Messages:
    6,843
    Thanks Received:
    1,638
    Location:
    Nottinghamshire
    Country:
    United Kingdom
    Isn't that the wrong way around? If the microswitch is stuck 'on' (i.e. the contact is closed) then both wires will be at the same potential (230V) therefore the voltage difference between them measured by the multimeter will be 0V.
     
    • Thanks Thanks x 1
  12. CBW

    CBW

    Joined:
    26 Sep 2019
    Messages:
    9,652
    Thanks Received:
    2,638
    Location:
    North
    Country:
    United Kingdom
    Edited - due to lack of accuracy
     
    Last edited: 4 Nov 2021
  13. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    23,966
    Thanks Received:
    10,066
    Location:
    Livingston
    Country:
    United Kingdom
    turn the power off, remove the two orange wires from the wiring centre terninal and test for continuity betwee the orange wires and the grey wires, one at a time, if one shows continuity, that is the faulty valve
     
    • Like Like x 2
    • Thanks Thanks x 1
  14. kidgreen61

    kidgreen61

    Joined:
    8 Mar 2009
    Messages:
    2,491
    Thanks Received:
    602
    Location:
    Staffordshire
    Country:
    United Kingdom
    ianmcd has nailed it.(y)
     
    • Thanks Thanks x 1
    • Like Like x 1
  15. soulcake

    soulcake

    Joined:
    4 Nov 2021
    Messages:
    5
    Thanks Received:
    1
    Country:
    United Kingdom
    Great, I’ll give that a try next thanks!

    I’m not sure if this helps at all, but I’ve had everything turned off most of the day and before turning everything back on to get some heat in the rads I turned down the thermostat on the hot water tank to its minimum at 25C (it clicked below 45-50). As soon as I turned the pump back on the valve on the pipe leading to the hot water tank opened. That’s with the thermostat on the tank turned down and no heating or hot water turned on at the controller. Would I be right in thinking that this might indicate the micro switch in the hot water valve as the likely culprit, or is that normal behaviour?

    I’ll see what I can do with a multimeter after there’s a little heat in the house and I turn things off again. Thanks again.
     
    • Thanks Thanks x 1
Loading...