Heatmiser Neo air thermostats

I'd be tempted to suggest that they run them as normal and have them all with their own batteries, one set of batteries to power multiples of these stats would probably be used up in no time, That being said, that many stats is a heck of a lot of batteries which may one reason they did it.

FYI - one to check - The default failsafe on the Air > RF controller is to switch that zone on for 12mins p/hr regardless, if the stat doesn't talk to it for 40mins, say when the batteries run out, unless they are all set not to in the settings, so if they all go off then all the zones would do it.
Hi

This is correct, they said the ufh in the bathrooms have been coming on due to the stats not working.
 
You can turn that setting off, but you've serviced the boiler and perhaps you are done.
 
Yep - To stop that then every stat would need changed. In the stats options menu, set the failsafe option (P3) to 0. How to set that will be in the manual. The client should be able to do that.

Or give every stat their own batteries I guess.
 