Can you point me in the right direction to resolve an ongoing lockout issue please?
Worcester Heatslave 12/14 oil boiler with Electro Oil Inter B9A burner.
Lockout is occurring after about 3 to 4 minutes. It is the same if water only or water and heating are called for. I have checked the oil filter - ok - and cleaned the flame sensor. Nozzle was changed six months ago.
Sequence is;
Reset lockout
8 seconds to flame.
Click of relay? after 3 to 4 minutes.
About 20 seconds to lockout light
About 45 seconds to fan stopping
About 10 seconds to click of safety device.
This happens time and time again.
Any ideas please?