Could any OFTEC installers please confirm whether a flexible oil supply line shoul have been installed from the regulator to the boiler, mine hasn't got this installed and I wondered if it was an OFTEC requirement??

Thanks :lol:
 
There should be a Flexible fuel line at the final connection to the Pressure Jet oil Burner, (to allow the burner to be removed from the boiler for maintenance, however in cased boilers, the flex should not extend out of the casing, it is also not normal to fit a flex to Vapourising type burners. :wink:
 