Hi,
New to the forum. I’ve recently qualified and past part P. Doing my first assessment and want everything to go right lol. Any issues please point out and correct while making fun of them.
Friend wants sockets and lights outside in his garden. (lights 2gang switch one for flood light and one for decking lights) and 3 sockets (socket run of approx. 30m one is at far end of garden).
CU (TN-C-S) in house and I’m going to use the only spare 32mcb (Non RCD) with 6mm T&E and run to a ‘garage CU’ (in house about 5m away, inside house, from old CU). Will be 40A 30mA RCD 2way with 20A MCB (radial for sockets) and 6A (lighting). He travels frequently and wants to be able to switch them off when he goes away to avoid them been abused).
6A with 1mm T&E for run of approx. 25m including all runs and switch drop
20A with 2.5 radial in conduit (in with 1.0 cable for first 10m in conduit) then approx. additional 15m in conduit for final 2 sockets (large distance between them).
Lengths will be ran in conduit along the house for lighting and first socket and by the side of fence along a wooden batten for the final 2 sockets (friend won’t pay for trench to be dug). There will be several bends throughout to get to the initial ‘starting place’.
4mm T&E makes the job double the price and would be cheaper to go to 32A ring rather than 4mm radial. Opinions on that??
Depending on Zs would consider 6mm earth to earthing block however due to short distance of the 6mm T&E linking CU’s I’m guessing it will be ok (or should it be done regardless).
Any advice or ‘look out for’s I’m happy to hear.
Thanks in advance. )
New to the forum. I’ve recently qualified and past part P. Doing my first assessment and want everything to go right lol. Any issues please point out and correct while making fun of them.
Friend wants sockets and lights outside in his garden. (lights 2gang switch one for flood light and one for decking lights) and 3 sockets (socket run of approx. 30m one is at far end of garden).
CU (TN-C-S) in house and I’m going to use the only spare 32mcb (Non RCD) with 6mm T&E and run to a ‘garage CU’ (in house about 5m away, inside house, from old CU). Will be 40A 30mA RCD 2way with 20A MCB (radial for sockets) and 6A (lighting). He travels frequently and wants to be able to switch them off when he goes away to avoid them been abused).
6A with 1mm T&E for run of approx. 25m including all runs and switch drop
20A with 2.5 radial in conduit (in with 1.0 cable for first 10m in conduit) then approx. additional 15m in conduit for final 2 sockets (large distance between them).
Lengths will be ran in conduit along the house for lighting and first socket and by the side of fence along a wooden batten for the final 2 sockets (friend won’t pay for trench to be dug). There will be several bends throughout to get to the initial ‘starting place’.
4mm T&E makes the job double the price and would be cheaper to go to 32A ring rather than 4mm radial. Opinions on that??
Depending on Zs would consider 6mm earth to earthing block however due to short distance of the 6mm T&E linking CU’s I’m guessing it will be ok (or should it be done regardless).
Any advice or ‘look out for’s I’m happy to hear.
Thanks in advance. )