    Hi Everyone,

    I’d really appreciate your help on this one. I realise that there are already lots of posts about wiring up a Hive receiver, but I still can’t get this sorted, so if any of you can advise me I’d be very grateful.

    I have a Worcester Bosch 70/90-000-NI-L oil fired boiler. It is currently controlled by a wireless Honeywell Digital Thermostat/Timer paired with a Honeywell BDR91 wireless relay box.

    I’ve installed the Hive hub and wireless thermostat no problem and I tried installing the single channel receiver. They all talk to each other OK and indicate that the boiler is on when it should be, but the boiler isn’t firing up. I’ve put the old Honeywell receiver back on and triggered it manually, and the boiler starts up correctly. So I think it may be to do with the wiring on the new Hive backplate.

    I’ve attached a photo and sketch of how the Honeywell is currently wired and of course the diagram of the Hive single channel backplate which has been posted on here lots already.

    I think the issue may be to do with the loop from A to L on the Honeywell receiver, but I’m not an electrician and have no idea how (or if) to replicate this with the Hive.

    Thanks in advance for your guidance.
     

    Attached Files:

  2. Sponsored Links
  3. muggles

    muggles

    Joined:
    28 Oct 2005
    Messages:
    12,955
    Thanks Received:
    2,914
    Location:
    Daventry
    Country:
    United Kingdom
    Loop L to 1 on the Hive
     
  4. PST

    PST

    Joined:
    28 Nov 2020
    Messages:
    6
    Thanks Received:
    0
    Country:
    United Kingdom
    Muggles
    Thanks for replying so quickly. Before I damage anything (or myself!) can I just check that this is what you mean?
    Thanks Hive Wiring.jpg
     
  5. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    21,903
    Thanks Received:
    8,610
    Location:
    Lanarkshire
    Country:
    United Kingdom
    yes that is correct, but you show the wire from 3 in the hive as blue , some others reading this post will assume it is a neutral, it is not , it is the switched live and should be Brown
     
  6. jackthom

    jackthom

    Joined:
    14 Feb 2007
    Messages:
    1,342
    Thanks Received:
    236
    Location:
    Northumberland
    Country:
    United Kingdom
    In the initial setup the brown was switched Live and the blue was Neutral. That doesn't match up to the new wiring.
    Is it installed in the same location?
     
  7. stem

    stem

    Joined:
    20 Jul 2005
    Messages:
    6,566
    Thanks Received:
    1,512
    Location:
    Nottinghamshire
    Country:
    United Kingdom
    This is how to swap the Honeywell for Hive, like for like.

    Wiring.jpg

    However. It appears that there is no permanent live going to the boiler shown in your diagram. Not all boilers need this, but it may be, that the boiler has a separate mains supply fed from elsewhere. If so, this is not ideal. Both devices (Boiler and Controls) would normally be supplied from the same fused supply.
     
    Last edited: 29 Nov 2020
  8. PST

    PST

    Joined:
    28 Nov 2020
    Messages:
    6
    Thanks Received:
    0
    Country:
    United Kingdom
    Thanks everyone for your help – this is a great forum!

    To answer Jackthom’s question, yes it’s a straight swap to replace the Honeywell receiver with the Hive single channel receiver.

    If I’ve understood correctly the attached diagram corrects the brown/live and blue/neutral from the boiler side. The difference between this and stem’s diagram is that you show the boiler blue/neutral connecting to the N terminal on the Hive, but I think other’s thought it should be connected to the 1 terminal.

    If I try one or the other until it works am I likely to damage anything?


    Hive Wiring Nr 2.jpg
     
  9. stem

    stem

    Joined:
    20 Jul 2005
    Messages:
    6,566
    Thanks Received:
    1,512
    Location:
    Nottinghamshire
    Country:
    United Kingdom
    That doesn't make a great deal of sense to me unfortunately. Hive Terminal 1 is a live, as is terminal 3 so you are sending a 'permanent live' and a 'switched live' to the boiler. There's no neutral shown going to there. And as others have said, this doesn't match up with your original diagram, which shows a 'switched live', 'neutral' and 'earth' going to the boiler

    We can only assist if you give us the correct information to work from.

    So, based on your original information, if this wiring schematic you posted is correct.....

    1.jpg

    .....then this is the like for like exchange using a Single Channel Hive

    2.jpg

    However, if your original schematic is not correct, then you need to provide the correct information, before anyone can advise.
     
  10. Sponsored Links
  11. PST

    PST

    Joined:
    28 Nov 2020
    Messages:
    6
    Thanks Received:
    0
    Country:
    United Kingdom
    Stem,
    Thanks for your help. The original schematic is correct. So I'll go with what you have shown above and report back.
     
    • Like Like x 1
  12. Madrab

    Madrab

    Joined:
    4 Oct 2012
    Messages:
    7,931
    Thanks Received:
    2,237
    Location:
    East Renfrewshire
    Country:
    United Kingdom
    Yep, You are confusing things with that blue wire. The only wire that comes from the hive to the boiler will be the brown switched live, from terminal 3. There is nothing to be taken from terminal 1,2 or 4.

    Is your boiler powered from a separate L/N/E from an FCU?
     
  13. ericmark

    ericmark

    Joined:
    27 Jan 2008
    Messages:
    17,930
    Thanks Received:
    1,670
    Location:
    Llanfair Caereinion, Nr Welshpool
    Country:
    United Kingdom
    This seems the correct version
    temp.jpg
    Note change to neutral wire, as said normally the supply is no simply plugged in, no reason it should no be plugged in other than chance it is then unplugged in error, normally use a single fused connection unit (FCU) for all central heating.

    When I moved into this house found 3 FCU's and a plug feeding the central heating some from a fuse box, and others from a consumer unit, it did not work correctly and was dangerous, and it seems unusual to have an oil boiler that does not also do DHW in some way. So I suspect there is some thing missing?
     
  14. stem

    stem

    Joined:
    20 Jul 2005
    Messages:
    6,566
    Thanks Received:
    1,512
    Location:
    Nottinghamshire
    Country:
    United Kingdom
    That's a good question, I mentioned it earlier. However not being overly familiar with oil boilers I looked at the circuits for a WB 70/90 on line, if you put the two diagrams below together, it appears that the only 'Live' connection that is required is a switched live from the controls, if this is the case a separate FCU isn't required.

    1.jpg

    @PST don't try to relate the above diagram to your actual installation, it's only been posted to show that the L terminal [Shown in the red box on both diagrams] is a switched live from the controls, and not a permanent live.
     
  15. PST

    PST

    Joined:
    28 Nov 2020
    Messages:
    6
    Thanks Received:
    0
    Country:
    United Kingdom
    Madrab, thanks for your comment. No, there is no other power supply to the boiler, only what comes through the wireless receiver.
     
    • Like Like x 1
  16. stem

    stem

    Joined:
    20 Jul 2005
    Messages:
    6,566
    Thanks Received:
    1,512
    Location:
    Nottinghamshire
    Country:
    United Kingdom
    Ha ha, our posts must have crossed in the ether. Looks like you're sorted now. Sorry if we confused you. :)(y)
     
  17. PST

    PST

    Joined:
    28 Nov 2020
    Messages:
    6
    Thanks Received:
    0
    Country:
    United Kingdom
    Thank you all for your help. It's all up and working correctly now thanks to your collective help. For the record, and for anyone who has the same issue, here's the final working arrangement. Stay safe everyone and have a great Christmas!
    Hive Final.jpg
     
    • Like Like x 1
  18. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page