You're welcome.
If you find these wires are in place, which is likely if the thermostat hasn't been touched at all, it's difficult to say what is going on at the other [timer] end of the wires as you haven't given any details of the timer, or its wiring connections. However, the T6360B thermostat should have 3 wires running out to it.
1) A live wire connected to T6360B terminal 1.
2) A neutral wire connected to T6360B terminal 2
3) And a switched live wire that controls the heating connected to T6360B terminal 3
It's possible that the the neutral wire hasn't been reconnected at the other end, in which case the thermostat will still turn the heating on and off, (albeit not as accurately as it should do) but the lamp will not light up. So what follows assumes that the thermostat is actually turning the heating on and off.
If you find that the neutral hasn't been reconnected and you wish to reinstate it; just a note of caution. Some installers will use blue wires as a live wire, so it will be necessary to find a neutral terminal and not just assume that any terminal with a blue wire in is the neutral.
Finally, if you do manage to get the light to work and find that it stays 'on' instead of switching 'off' when the thermostat turns the heating off, the live and switched wires have been transposed. Should this happen post back for further assistance.