Indeed - but surely the question is whether, if the armour is used as the sole CPC, the Zs of the circuit will be low enough for ADS (to protect 'everything'). That is what the on-site electrician needs to ascertain.Whilst everything that has been said may be correct, surely if the armour is adequate for ADS and protection of the cable then it is adequate for ADS to protect the hot tub and occupants.
Yes, agreed.That is what the on-site electrician needs to ascertain.
. I don't understand. Missing out the middle clause, my sentence would read "... the question is whether .... the Zs of the circuit will be low enough for ADS". Do you disagree with that?I don't think you have worded that very well. The other way round, surely.
Fair enough, but that's not how I read any of the comments.I got the impression people were saying it would NOT be - yet good enough for protection of the cable.
You said:. I don't understand. Missing out the middle clause, my sentence would read "... the question is whether .... the Zs of the circuit will be low enough for ADS". Do you disagree with that?
Exactly.Fair enough, but that's not how I read any of the comments.
TTC might have confused things a bit my mentioning adiabatic calculations. I very much doubt that such a calculation would indicate that the armour was at any risk of melting under fault conditions (particularly if the Zs of the circuit was 'too high'),
So, it may not be suitable for ADS protection of the cable, either.BUT it remains possible that the Zs of the circuit would be too high for ADS.
Perhaps, but that doesn't alter the correctness of my statement!You said: "but surely the question is whether, if the armour is used as the sole CPC, the Zs of the circuit will be low enough for ADS (to protect 'everything')." Yes, but it is determined the other way round. Zs first and then whether the armour can be so used.
Indeed. I think some people make the mistake of thinking that just because it has 'earthed armour', SWA is always 'adequately protected', regardless of all else. However, if the armour is being used as CPC, then the impedance/resistance of that armour forms part of the Zs - so if the cable gets long enough, the Zs will be too high for ADS in the event of an L-armour fault at the end of that cable.So, it may not be suitable for ADS protection of the cable, either.
You're probably right. The more common discussion is whether the armour is adequate as a bonding conductor, and the answer to that is far less of a foregone conclusion.I think it extremely unlikely the armour may not be used as the CPC ...
Yes, that's what I said in my first reply because I thought it was being confused with the CPC.The more common discussion is whether the armour is adequate as a bonding conductor,
Fair enough.Yes, that's what I said in my first reply because I thought it was being confused with the CPC.
There are.Of course, there are factors other than the measurements (when the cable is installed) which make some people reluctant to rely upon armour as the only CPC.
Anything is possible.Although rare, it can happen that a breach in the outer sheath allows water in - which, in turn, may eventually lead to corrosion and the complete or partial disintegration of the armour at the point in question.
It is.Unless the whole cable gets 'chopped', it's all-but-impossible that a core of SWA being used as a CPC could suffer isolated damage.
I'm not surprised.I must say that I've always been in the "don't rely on armour" camp, but I realise that opinions vary, sometimes strongly.
I didn't notice anyone saying that it was 'unsuitable', but I did see several people say that an electrician needs to check that it is suitable. As you go o n gto say ....H o w e v e r , the OP said he had 10mm² two-core and I thought people were suggesting that this was going to be unsuitable when, in fact, it may not be.
The OP should and must employ an electrician as outside power is not, in my opinion, a DIY job.
I'm not bernard, you know - and if you hadn't worked it out, what I 'preach' and what I practice are often too very different thingsI'm not surprised ...... As a matter of interest, as you are extra safety-conscious, would you, as a personal preference, TT a hot tub in the garden regardless?
Ah. No wonder you seem contradictory at times and we get confused.What I often do do is "play Devil's Advocate", in order to make sure that a balanced picture of a range of opinions is presented to readers.
... but you do, don't you because of the water pipe?As for your question, in my house the question would not really arise, since it's hard to think of any credible scenarios in which 'exporting' a TT earth would do any harm. However, if I had TN-C-S, I would give at least some thought to bernard's view.
My view has always been that, when there is a range of opinions (or interpretations of the regs), then it is important that DIYers are presented with the more 'cautious' ('safety-conscious') ones, as well as the others. If no-one else has done it, I will therefore often presnt those 'cautious' opinions (usually preference by something like "Some people feel/believe...."), even if they are 'far more cautious' than I would ever contemplate doing myself, in my home.Ah. No wonder you seem contradictory at times and we get confused.
Ah - are you talking about my 'quasi TN-C-S earth? If so, I suppose you have a point, so maybe I should have said "if I had a 'pure' TT system"!... but you do, don't you because of the water pipe?
I can understand that viewpoint, which I suppose one could probably call "bernard's view". In those very rare 'neutral fault' condition, the problem with an exported TN-C-S (as with a metal-plumbed outside tap) arises if it is possible to stand (maybe with bare wet feet) on ground at roughly true earth potential outside the outhouse (hence outside of the equipotential zone) whilst simultaneously touching something within the equipotential zone - a metalclad light switch just inside the door of the outhouse would be an example.I asked because I am frequently puzzled by people, not necessarily on here, who, when asked about outside power to sheds etc., state that they would TT it out of preference as a matter of course - even if extending the equipotential zone was not a problem.
Maybe at least some of them do "do something about the tap on the wall"? After all, it only needs a couple of inches of plastic pipe to eliminate the potential 'problem'.Yes, I realise that, BUT - if no one ever does anything about the tap on the outside of the house, why do they feel it is different with a shed?