Went on a breakdown tonight and this was the boiler.
They said it hadnt worked since friday, and was working fine before that
When I got there, the fan was stuck, so eventually managed to free it and got it going with some wd40
It then lit the pilot but when going to full gas (which it didnt), there was a banging noise coming from the gas valve.
I took the leads off of the second solonoid and got a reading of 230V, Then switched boiler off, put leads back on and it went to full gas. Switched off and tried again and the banging was back and it wouldnt go to full flame
Anyway, eventually after switching it on and off several times it went to full gas so I left it and recommended a new gas valve, is this correct? There isnt anything else that would affect the gas valve in this way is there?
Thanks