Just want to double check, on a boiler which won't reset clear the voltage to the gas valve measures 108V DC, with 240AC (which may be residue). The manual states it should be 200V, others say 150V is fine. Is 108V not fine?
The boiler immediately faults which leads me to believe PCB. There's no water ingress and no dry joints.
The boiler immediately faults which leads me to believe PCB. There's no water ingress and no dry joints.