Hi, im currently working on an ideal isar 30he and im finding it a bloody nightmare.
Step 1: Turn boiler on, ask for heating and the fan runs
Step 2: gas valve opens and the boiler ignites
Then within a 10 seconds the boiler starts to humm and shake, gas cuts out and it re does the procedure above 3-4 times and then cuts out with an l-f fault.
the boiler has a new orange pcb fitted, condensate traps are completely clean and so is the trap. sump is completely clean, fan is not making any weird noises, flue is clear, electrodes have continuity when checked with meter and gaps are fine.
I rang ideal and they were no help what soever, they told me it could be the gas valve. so i wanted to know if any1 else has experienced this sort of problem. all help will be appricated, and if i find the problem with it i'll post it up to help others