MY BOILER WOULD NOT LIGHT IGNITER NOT WORKING THE AUTOMATIC IGNITER BOARD RELAY WAS ALL BURNED I GOT NEW BOARD BUT NOW NOTHING NOT EVAN THE FAN IS WORKING THE NEW BOARD HAS A LINK IN IT CAN ANYBODY TELL ME WHAT THIS LINK IS
What terminal numbers are linked? These links are normally where external controls are connected ie room stat etc.Make exactly the same connections as were on the old board.Have you checked that the overheat has not tripped?
this boiler is not fitted with thermostate or time clock i had new controller fitted the main connector strip beside the board at top it has mains in from that a feed is taken to the controls L and L1 has pair of wires up to 1 and 3 inside controller
If you have just replaced the ignition pcb all you need to do is to disc 5 plugs and the ignition/detection wire and simply replace in the same positions on the new board.All the wiring to the 12 way connector remains the same.You need not alter any of these connections.