I'm confused about junction box rules

No one bothers when a ring is extended but people don't like multiple spurs in say 4mm, strange ay :giggle:
 
I think it means "farthest" but apart from that I cannot add anything.
I would be very surprised if you had not made that comment, but I can assure you that I copied/pasted the exact text from the OSG - so don't blame me :)
I'm just surprised I hadn't realised before how silly the was requirement was.
It does seem totally ridiculous, but I can't think of what on earth could have been going on in their minds to cause them to write that - and even more surprising that, in more recent times, no sensible person has come along and removed it. There surely must be at least one sensible person involved with the writing/revising of the OSG, mustn't there? :)
 
Very good question but, as I've just observed, that persists in today's OSG ... and, even worse, it still has ...

What on earth is that all about?
@securespark - was that ever in the regs?
I haven't seen anything on my travels through all the old regs and guides I have. Having said that, I haven't by any means read all of them cover to cover.
 
Exactly - as I said, that's what I've always assumed - but, as I pointed out, it leads to ridiculous situation

Yes - but, as I wrote, even if it is a very long ring, spurs originating anywhere near the midpoint of the ring would be allowed to have little (or, ultimately, NO) length :)
That doesn't make sense?
 
Exactly - as I said, that's what I've always assumed - but, as I pointed out, it leads to ridiculous situation
EDIT: But thinking about it further that would mean for a ring of 100m the restriction would be 6.33m but a really tiny ring of 8m (yes they can just about exist) only 0.5m. Which would be somewhat counter intuitive to me. it kinda feels like it should be the inverse.
Yes - but, as I wrote, even if it is a very long ring, spurs originating anywhere near the midpoint of the ring would be allowed to have little (or, ultimately, NO) length :)
Oops. my interpretation was the longer the ring length the longer the permissible spur length
IE 1/16 of 100m = 6.33m anywhere on the ring... which I what I believe I've seen before and therefore only skimread your post

but
1760719456126.png
is very different to that and quite frankly meaningless other than the L/N impedance is highest at midpoint and as such adding a spur will increase that further.

My gut feeling without any calculations or fag packet sketches is:
At 75% round the ring a spur of length 1/16th of the ring will result in the same Z at the centre
At the origin a spur of length 1/4 of the ring will result in the same Z at the centre. However adding that at the 50% position will double the Z

Apo;logies if mythoughts are too irrational :unsure:
 
I haven't seen anything on my travels through all the old regs and guides I have. Having said that, I haven't by any means read all of them cover to cover.
Thinking about it, the obvious thing is to limit Zs.
 
That doesn't make sense?
Indeed, it's crazy. Interpreted in that way (which seems the most obvious/likely), it means that if, say, one took a spur from a socket which was right in the middle of the ring (the 'best' place to originate a spur), the maximum permitted length of that spur would be zero !! ... and not a lot better for spurs originating fairly close to the middle of the ring!
 
Oops. .... only skimread your post

but View attachment 396100is very different to that and quite frankly meaningless ....
As I've been writing it (and its consequences) seem pretty crazy to me!
other than the L/N impedance is highest at midpoint and as such adding a spur will increase that further.
It will (for the spurred socket) and one obviously theoretically ought to determine (by measurement or calculation) the Zs at the end of the spur to make sure that it is low enough. However, this arbitrary rule of thumb (which means that one is not allowed to have a spur originating at, or close to, the midpoint of the ring) is surely not an acceptable alternative to actually measuring or calculating the Zs?
 
Thinking about it, the obvious thing is to limit Zs.
It's as good a theory as any other I can think of but, as I've just written to Sunray, I really don't think that this arbitrary 'rule of thumb' is a particularly acceptable approach, particularly given that its effect appears to be to prohibit spurs which originate at, or close to, the middle of the ring!)
 
Oops. my interpretation was the longer the ring length the longer the permissible spur length
IE 1/16 of 100m = 6.33m anywhere on the ring... which I what I believe I've seen before and therefore only skimread your post

but View attachment 396100is very different to that and quite frankly meaningless other than the L/N impedance is highest at midpoint and as such adding a spur will increase that further.

My gut feeling without any calculations or fag packet sketches is:
At 75% round the ring a spur of length 1/16th of the ring will result in the same Z at the centre
At the origin a spur of length 1/4 of the ring will result in the same Z at the centre. However adding that at the 50% position will double the Z

Apo;logies if mythoughts are too irrational :unsure:
FWIW applying the 1/8 from the centre point rule: In order to make calculations easy I've assumed a ring resistance of 64 32Ω and zero source resistance- yes I know unrealistic but can easily be scaled to any real value, the following sketch shows the ring L+N resistance and end of spur L+N resistance at various points
1760751017915.png
The 1/8 rule prettymuch limits the end of spur resistance to the maximum of the ring
 
Last edited:
Gosh this thread has run and run

Back to the OP - I too believed what was written and that the spark was told what the plans were

So I just think the spark used what he had to hand and nobody would question it rather than using the correct part from the get go

I am now retired BUT always carried traditional JBs and MF JBs in my van for these very situations
 
Thinking about it, the obvious thing is to limit Zs.
Yes, on reflection, as you and Sunray have said, Zs is fairly obviously what it was about.

However, one cannot say anything about the maximum permissible length of a spur from a ring (Zs-wise) without knowing, or making some assumption about, the Zs of the ring itself (highest at mid-point of ring).

It seems that, at least for some purposes, they have assumed that Zs at the mid-point of the ring was already the 'maximum permitted' - in the sense that that explains why the stated 'rule of thumb' does not allow a spur of any length at the midpoint of the ring (and makes permissible spur lengths impractically short near to that midpoint).

However, what I still don't get where their "one-eighth" comes from. I haven't got time at the moment to do the proper sums, but will later. However, for starters, assuming that the mid-point of ring is already at 'maximum Zs', it would seem that a spur originating very close to (or even 'at') the origin of the ring (in same size cable as ring) could have a length equal to one-half (not one-eighth) of the distance from that point to midpoint of ring and still have a 'just OK' Zs, couldn't it?

More later, when I have a little time to look in more detail at the numbers.

Furthermore, and more to the general point, if it were a small ring, with a Zs at midpoint well below the 'maximum Zs', it would be possible (Zs-wise) to have a much longer spur than the rule-of-thumb indicates - ultimately potentially longer than (let alone 'one eighth of') the distance from spur to midpoint of ring!
 